opaone

Range Hood Noise Project

opaone
3 years ago
last modified: 2 years ago

The purpose of this thread is to collect information on the loudness of various range hoods.

The EU requires that all manufacturers publish standardized noise ratings for all hoods for lowest, medium and highest speeds. Unfortunately we do not have this information for hoods sold in the U.S. but we can collect it ourselves on this thread to get a realistic idea of how loud various hoods and configurations are. FWIW, the EU recommends that exposure to noise levels above 53dB(a) be limited to no more than 4 minutes.

To stick w/ EU standards;

  • Measurements should be taken 1m (3' 3") from the front of the hood, 1.75m (5'9") from the floor.
  • Measurements should ideally be done with 'Decibel X' or 'Decibel X Pro' on a recent iPhone (Ideally 8 or newer) if possible. Secondarily on an Android or older iPhone.
  • Stand with the iPhone facing perpendicular to the hood with the iPhone held roughly at arms length. E.G., if you are facing your iPhone then your hood is to your left or right. iPhone should be at about the center of the hood.
  • Measurements should be done in dB(a). E.G., not dB(c)
  • Ideally measurements should be done when there is no other noise. If Ambient is below 32dB(a) that's ideal but I can adjust for higher.
  • Please take 5 measurements; Ambient noise level (hood not running), Hood Low, Hood Med, Hood High, Ambient noise level again. If you can please give a 15s avg as well as peak.

We already have data on four hoods collected in the Hood FAQ and Commercial Hood Install threads. I'll collate the data in a spreadsheet and post a chart in this thread periodically.

Thanks for your help!

Comments (64)

  • kaseki
    3 years ago

    LD 10 silencer data I have from Fantech is as follows. dB (attenuation) @ f (Hz)

    • 6@125
    • 11@250
    • 21@500
    • 27@1000
    • 39@2000
    • 25@4000
    • 19@8000

    Apologies for not making a table and turning it into an image. I think the values for the entire line are somewhere on Fantech's web site.

    I would describe these values as being aimed at fan blade and duct turbulence noise frequencies and not so effective at motor vibration frequencies. The latter might be transmitted via the duct skin, so the silencer would not be an appropriate device for vibration attenuation.

    opaone thanked kaseki
  • opaone
    Original Author
    2 years ago
    last modified: 2 years ago

    Here’s a very very quick version of the chart in Sones (converted from dB(a)). Note that while dB or dB(a) is an objective measure, Sones is subjective. More to come.



  • Related Discussions

    Z line range hood - more than TWICE the decibels - why so loud?

    Q

    Comments (8)
    A few thoughts... - Many noise apps are not very accurate. Most accurate we've found in our lab is Decibel X on an iPhone 8 or newer. Make sure you are using dB(a), not dB(c/z), are 1m from the hood, etc. More on how to accurately measure: https://www.houzz.com/discussions/6040827/range-hood-noise-project - Duct and blower should be mounted with strap and NOT ever come in contact with framing or other elements that transmit vibration noise and effectively turn your house in to a giant speaker. - Yes on duct possibly being too small. If so then this will result in increased noise. - Bends/Turns (w/ proper sized duct) are actually good for noise reduction even if not so good for overall performance. - Distance to blower is good for noise reduction. - A duct silencer between the hood and blower can be very helpful. - 1200 CFM is a lot for such a small hood. You likely have a lot of noise just trying to pull a lot of air through a small baffle. - Baffle design has a big impact on noise levels. Many consumer hoods do poorly on this. How loud is it w/ baffles removed? - Your hood lacks sufficient containment volume which requires you to operate at much higher CFM's (and thus greater noise) for the same (or worse) effectiveness at effluent removal. - Blower may be out of balance. Not necessarily noise related: - Your hood looks the same width as your range. The aperture/opening s/b at least 6" wider than your range and ideally at least 27" deep.
    ...See More

    Is a 48" range too big for our space?

    Q

    Comments (38)
    Well, reading this thread was an enjoyable interlude, although I'm not sure that there wasn't any schadenfreude hiding in my unconscious. As I don't have an iPhone to use to provide noise measurement consistency with @opaone's noise measurement request, all I can say about my 1500 nominal CFM system is that it certainly is noisier than my SubZero 632, or my Miele Optima (especially when it's broken), but not so noisy that one can't talk across or along it with a reasonably normal voice level. At 3 times the person-to-person distance (R^2 = 9), a TV source needs to be made louder to hear with the same clarity as when the hood system is off, if the listener is under the hood edge. @Indecisiveness: For both residential hoods and commercial hoods designed using the Greenheck method, air velocity is where its at. However, there is a significant difference between the values needed. In the case of the residential hood, which I have (Wolf Pro Island hood), there is a need to immediately entrain the rising effluent into the air flow passing into the baffle gaps. In the much taller commercial hood, there is a large air volume reservoir below (and often beside) the baffle assemblies that allows CFM averaging (I call it) over the baffle space. Due to height and shape, commercial hoods allow the effluent velocity to slow down. As a result, the necessary specific hood entry aperture air flow (ft/min or CFM/sq. ft.) can be lower for a given spillage threshold. See images. Lower air velocity means a less noisy hood system, and with care, a less noisy MUA system. Opaone's baffle gap air velocity should be lower than mine when dealing with the same effluent. The effluent path to his hood's baffles is likely 5 to 6 feet above the cooktop, whereas to mine it is about 3 to 4 ft (angled baffles). His hood is large enough to encompass the rising and expanding effluent at commercial hood height. All that is physically needed for a commercial grade system is sufficient kitchen ceiling height and a decent passage space to the outside for hood system and MUA system. Compromise to residential configurations is basically driven by architecture and aesthetics, if funding is sufficient. Spillage vs. no spillage from a griddle to a commercial hood; difference is specific air flow. (The image is showing schlieren photography heat imagery, not steam.)
    ...See More

    xo hood need advise to meet local building compliance

    Q

    Comments (7)
    Jennifer: A semi-pro stove requires a semi-pro ventilation system, and the costs will be commensurate. You or someone you trust will have to do the ventilation research. Most of the principles and formulations that you will need to know have been presented on this forum for more than a decade. The review will take some time but it will be worth it in venting performance and noise minimization. To start, here are some recommended links: The "Greenheck guide" first dozen or so pages https://www.tagengineering.ca/wp-content/uploads/2015/02/KVSApplDesign_catalog.pdf Some threads of note on this and the HVAC forum: https://www.houzz.com/discussions/2328297/range-hood-faq-personal-notes-updated-10-31-2007#n=20 https://www.houzz.com/discussions/5161173/hood-faq#n=101 https://www.houzz.com/discussions/6099827/exhaust-hood-faq-ii#n=113 https://www.houzz.com/discussions/6040827/range-hood-noise-project https://www.houzz.com/discussions/5888450/seeking-muas-advice#28657635 And opaone's quasi commercial adaptation for his residence with emphasis on indoor air quality: https://bamasotan.us/range-exhaust-hood-faq/ Searches will provide many more helpful messages. Once you have internalized this material, you will understand why simple "buy this" advice cannot be provided without a lot of additional information from you, informed by your reading.
    ...See More

    Shopping for a range hood? Need help!

    Q

    Comments (8)
    Perhaps I should add these comments: Commercial kitchens, such as restaurants, have kitchen ventilation operating cost as one of their main cost drivers. So they optimize on capture and containment performance vs. operational electrical cost. For residences, this is not usually an issue, so the trade space is bounded by the three factors: performance, aesthetics, and acquisition/installation cost. You won't get high performance and great aesthetics (buyer determined) at low cost. Either pick two of the three to maximize, or trade among them. No air leaves the kitchen via the hood system that hasn't entered the kitchen either incidentally (including wall leakage) or via a deliberate make-up air (MUA) system (simple or complex). Commercial units typically operate at one or a few air flow rates against which the MUA can be easily balanced. For residences with potentially multiple exhaust fans and a hood often operated over a variable range of flow rates, the residential MUA system may have added complexities over a commercial one. Further, code enforcement doesn't care if you gag your hood and fill your house with cooking effluent, code enforcement cares whether you pull a weak vacuum with the hood and back-draft combustion appliances, thereby pulling carbon monoxide into the house air. So at some point a search here on 'MUA' is recommended. In addition to many MUA threads on this forum, there is also a relevant one on the HVAC forum: https://www.houzz.com/discussions/5888450/seeking-muas-advice#28657635 Last, or first, the adoption of commercial elements into residential cooking ventilation may have merit for some, depending on space available and cost, so there is this link to ponder: https://bamasotan.us/range-exhaust-hood-faq/
    ...See More
  • opaone
    Original Author
    2 years ago

    BTW, conversion to sones is actually only good (or pseudo good) up to about 70 dB(a) or 19 sones. Beyond that is a different world.

  • tassadar
    2 years ago

    What are the specs for the various liners you list in the chart? Am curious to especially know the blower location and duct size. Thanks, such good info!

  • opaone
    Original Author
    2 years ago
    last modified: 2 years ago

    @tassadar, The Accurex, Modernaire and Wolf all have a remote blower and a silencer between the hood and the blower. I believe the Wolf is @kaseki's so he can perhaps provide some details.

    The Accurex is detailed here: https://www.houzz.com/discussions/5745986/commercial-range-hood-install

  • kaseki
    2 years ago

    I can only provide qualitative noise comments w.r.t. the Wolf Pro Island hood, 10-inch duct, Fantech silencer, and Wolf (Broan) 1500 CFM roof blower. I did not provide any numerical noise measurements, although I have provided some preliminary air flow data, possibly into Hood FAQ [I].

  • opaone
    Original Author
    2 years ago

    The Wolf data must have come from someone else then. Argh...

  • kaseki
    2 years ago

    Possibly @clinresga, if you took it from an old thread. Otherwise, maybe you got a PM and its still available. I can't recall any recent thread with a value that I would want to know for my own system.

  • opaone
    Original Author
    2 years ago

    Quick note that the charts above should read "/1000 CFM" rather than "/100 CFM".

  • kaseki
    2 years ago

    [From a submission on another thread: https://www.houzz.com/discussions/6251855/vent-a-hood-liner-vent-for-sale#27666135]

    Perfect is the enemy of good enough, but so also is too simple (excessive avoidance of complexity). On the basis of the comments in the thread referenced above, I concur that it might be best to just establish a table of rows by specimen measurement, with columns by manufacturer, model, blower rated CFM, duct length and diameter (if known), use of a silencer (if known), MUA type (if known). Then users will have to find cases closest to their intent and try to extrapolate to their specific case. Otherwise, we need a lot of fan curves (flow vs. pressure) vs. power level vs. sound level (dBa at 1m or whatever). The required complexity is mind boggling if one wants to try to determine a close result -- not unlike the complexity of estimating adequacy of a given hood over various cooking activities without running a full computational fluid dynamics analysis of the hood and MUA systems (plus extraneous room drafts and turbulence).

    Good luck and best regards @opaone!

  • opaone
    Original Author
    2 years ago
    last modified: 2 years ago

    From: https://www.houzz.com/discussions/6251855/vent-a-hood-liner-vent-for-sale#n=25

    "It isn't likely to be sones/1,000 CFM either. Discuss with @kaseki to understand why. You are still presenting something as linear, which is unlikely to be linear."

    In the first chart I presented dB(a) which is log. There is nothing we can do about that being log because dB(a) is indeed log. As far as I know the data in that chart is as accurate as possible with the limited data that we have.

    Presenting dB measurements to an audience unfamiliar with log measurements is problematic. I was a touring FOH engineer and studio engineer for about 10 years. I have a generally good concept of what the difference in 66 dB(a) and 69dB(a) is. I know how much louder that is. Most consumers though think it only 5% louder - relatively imperceptible.

    So, in the last chart I presented Sones. Sones is, IMO, a horribly inaccurate number but it does do a much better job of conveying noise experienced to people who are not accustomed to log scales.

    "Whoever made the chart manipulated the data and likely did so incorrectly. I suspect the they ran each hood on its highest setting and took a measurement. Then divided that measurement by that CFM and then multiplied by 1,000 CFM. That doesn't work unless the slope is linear."

    That is indeed the calc. Please tell me why in this instance that doesn't work. FWIW, this is exactly how the data is calculated and presented in the EU except that they have more accurate base measurements than we have.

    "The best thing to do is present the actual unmanipulated test results and let people see the raw data rather than trying to adjust to hold CFM constant.

    That is exactly what is presented in the first chart above and here: https://bamasotan.us/range-exhaust-hood-faq/

    FWIW, marketing people love to take advantage of consumers lack of understanding of dB log scaling. The raw data 'our hood is ONLY 6 dB louder but much more powerful than competior B' sounds great to unsuspecting consumers who don't have a concept of just how much louder 6 dB really is.

    Or you can find the actual logarithmic sound curve of each hood and then adjust them to some common CFM's to see quietest, but with only two data points on some models that doesn't seem likely."

    I think that would be great if you would like to do it or fund it. IIRC it's about $12k per hood measured for EU compliant measurements.

    -------

    @bry911, that I have seen you like to swoop in and offer a lot of critique, some useful/accurate, most not, but you never or rarely offer anything of positive constructive value. You waste a lot of my and others time replying to your innane posts.

    You like to sound like you know what you're talking about (I'm guessing that you are a lab tech?) but as soon as you get backed in to a corner or asked for detail to support your positions you disappear.

    This is all being done with $0. We have very limited data of questionable accuracy to work with.

    Likely the best noise data is my hood since we know exact actual CFM measurements for it and exact sound measurements.

    But that is of limited benefit without similar data on other hoods for comparison.

    We can only guess at the actual CFM rates of other hoods. I know from conversations with energy auditors who've measured them in homes that better than 50% of rated is extremely rare and many are closer to 20-25% of rated with some below 10%.

    Even if we had hyper accurate CFM measurements for other hoods that would still be of somewhat limited beneift as what we really want to know is extraction efficacy.

    As I've told you before, if you want to offer something constructive then I'm all ears.

  • opaone
    Original Author
    2 years ago

    @kaseki: "Perfect is the enemy of good enough, ..."

    Yes.

    This can all get much too complicated. I'm trying to find a balance between enough information and not too much.

    There is also a question of how accurate the base information is. As you pointed out we have little to no clue what the static pressures are on the supply and exhaust sides of the blowers nor what the actual CFM rates are. Extra decimal places aren't very useful if the accuracy of the measurements can't support it :-)

    When I get time, hopefully this weekend, I'll see about sticking either the table of raw data in the FAQ or adding the data to the first chart.



  • bry911
    2 years ago
    last modified: 2 years ago

    @opaone said, "@bry911, that I have seen you like to swoop in and offer a lot of critique, some useful/accurate, most not, but you never or rarely offer anything of positive constructive value. You waste a lot of my and others time replying to your innane posts."

    Let's tackle this little gem first. We started this discussion when you posted this nugget of wisdom on a thread someone started to sell a hood that had minor damage that they found unacceptable. "VAH is kind of the loud and noisy dog of hoods that most people don't want."

    Let's be clear. Vent-A-Hood is one of 10 companies with greater than 5% share of the residential ventilation hood market, which is a $4.45 billion market. To say that people don't want Vent-A-Hood is a ridiculous assertion, as they still sell a lot of them. All you were doing is trying to jump in there and act superior and add no real value.

  • bry911
    2 years ago
    last modified: 2 years ago

    @opaone - With all due respect, you consistently misinterpret data when trying to make it more impactful. The last time I pointed this out, you proved unwilling to listen regardless of the effort I put into explaining.

    In that case you represented an increase in the risk of illness as an increase in illness. Those differences may seem subtle, but they are tremendously important. Buying a lottery ticket increases your chance of getting rich, but you don't get richer every time you buy a lottery ticket.

    ----

    I have no desire to go a bunch of rounds on this. I will endeavor to explain but I have no interest in turning this into a debate.

    This is a fine chart:



    There is nothing wrong with this chart as it gives the measurements. However, the chart above can't be converted to this chart below:



    The problem has nothing to do with sound pressure being logarithmic, or decibels versus sones. The problem is that you don't know that the increase in sound to CFM is linear. I will endeavor to explain this in the following chart.



    My line is just made up... but so is yours. Just because it produces about 62 dB(a) when running at 1000 CFM, doesn't mean it produces 31 dB(a) at 500 CFM. It doesn't matter that dB(a) is logarithmic, you have no data to establish the actual function of dB(a) to CFM (log of logs are quite common).

    ----

    I think you are trying to demonstrate the noise efficiency of various hoods at max CFM, but that is not what your chart says. Nor would I, as someone who has to present data analysis in published research, attempt to visually represent that analysis. It is too likely to be misread as exactly what you presented even if you corrected the title.

    Good luck.

    ETA: I am sorry for the combative tone in the beginning, this post is certainly colored by our previous interactions. I am happy to help you improve this thread, and/or your blog. However, I am fairly busy right now and if your intention is simply to prove me wrong, I will happily concede defeat right now and move on.

  • opaone
    Original Author
    2 years ago
    last modified: 2 years ago

    "The problem is that you don't know that the increase in sound to CFM is linear."

    It doesn't matter. These are single point measurements.

    "My line is just made up... but so is yours. Just because it produces about 62 dB(a) when running at 1000 CFM, doesn't mean it produces 31 dB(a) at 500 CFM."

    I have not made up a line nor presumed a line nor presupposed a line. These are single point measurements.

    FWIW, if we produced a similar chart with as equal of CFM's as we can guesstimate (presuming that low CFM's is about 50% of high CFM's which is by engineering necessity the case w/ most baffle designs and we do have measurements for low for most of the hoods) it would make the VAH and Kobe look much worse and the others much better. VAH would not change at all but Accurex would be 0 ( dB(a) or sones, take your pick ), Modernaire, Wolf and Prizer would be lower, Kobe would remain about the same. If, as you stated I "misinterpret data when trying to make it more impactful." then I would certainly have done that but I didn't because I'm trying to keep it as simple as possible and simple conveyed the point.

    ----

    @bry911, this is similar to previous times you've made such critiques. I think you have some surface level understanding but you don't understand the underlying principles nor science. Nor do you have a good understanding of statistics or data presentation.

    I apologize for being so direct but I believe this is the third or fourth time you've made all kinds of critical comments without anything to back them up and for all of these you have yet to add anything constructive beyond possibly a typo.

    I, @kaseki and the others who have been working on this and related topics greatly appreciate valuable input but your input has been of no positive value and has actuallly wasted a lot of people's time.


    "However, I am fairly busy right now"

    Good.

  • vinmarks
    2 years ago

    These charts only list the manufacturer name and no model numbers. Are these the most recent hoods put out by the manufacturer and what models are they? You installed an accurex with a silencer. Was a silencer used to come up with the noise rating for accurex in that chart? Were the other hoods tested using silencers? How many hoods were tested of each model to come up with the chart? Who did the testing? Did they use the same equipment to measure the sound? Were there any other variables not taken into account such as silencers, remote blowers, duct length, duct size etc? Was the testing done in a controlled environment?


  • bry911
    2 years ago
    last modified: 2 years ago

    @opaone said, "this is similar to previous times you've made such critiques. I think you have some surface level understanding but you don't understand the underlying principles nor science. Nor do you have a good understanding of statistics or data presentation."

    Says the person who also says, "I have not made up a line nor presumed a line nor presupposed a line. These are single point measurements."

    "dB(a) per 1,000 CFM" is not a single point measurement. It is quite literally a slope. Since we know that hoods make 0 noise when off, it is a formula for a line. You don't understand the difference between a point and a slope and are attacking my understanding of data analysis.

    Let's see if we can demonstrate the difference with an unrelated example. Miles per hour (mph) tells you how far you will drive in an hour at that speed. So if we were driving 62 mph for 1/2 an hour we would drive 62*1/2 miles, which equals 31 miles. If you know the mph, we can plug in any number of hours and get the distance.

    Your second chart gives dB(a) per CFM. In other words your chart says that total dB(a) = dB(a)/1,000 CFM * CFM. It is wrong. This is middle school level Cartesian plane stuff.

    I believe @kaseki sees the mistake and agrees with my assessment but was trying to be polite.

    ETA: Just to be clear. Slope is rise over run. Any time you see "per," you have a slope.

  • bry911
    2 years ago

    Despite the aspersions, I do understand statistical analysis. I have spent an unfortunate amount of time working in R, which is made worse by time spent learning Stata.


    There are massive problems with the analysis in this and I normally wouldn't post it, but given the serious issues with the analysis presented in this thread...

    https://m.youtube.com/watch?v=AYvzb3VoS-I

  • kaseki
    2 years ago
    last modified: 2 years ago

    I think it is a well-meaning attempt at normalizing performance of examples for comparison that is fraught with hazard due to its potential for misinterpretation. And as we see, it is fraught with hazard due to its potential for argument. I have to admit that I didn't give it much thought before this argument blasted its way out of its crypt.

    Getting time to measure in my kitchen is problematic at present, but my intent is to measure SPL vs. actual measured air flow rate (at one point under the hood) to reveal what the relationship is for my particular configuration.

    My air speed sensor will be the one I described in Hood FAQ I.

    My sound sensor will be an early Radio Shack 33-1028 meter that was sold to me by my then employer as scrap test equipment. It may have hidden modifications. I intend to assume that nothing was done to make its relative measurement defective. I don't have a 'smart' cellular telephone that I can put an SPL measuring app onto.

    Note that this meter is unweighted, not "A" weighted, but historical frequency-response reports suggest that the effective weighting is "C" due to the microphone. "A" weighting fits the human loudness curve only for weak sounds. If my hood were as quiet as my Miele dishwasher, then "A" weighting would be a good filter function. "C" is probably better for noisy hoods, even if some clueless government factotum decreed that everything everywhere should be measured in "A" weighting, even the whomp-whomp of wind farms.

    For dealing with the ambient, it is probably best to convert dB into pascals, rms, and assume the background adds in quadrature to the hood noise, assuming my ambient is high enough for this meter to read it.

  • opaone
    Original Author
    2 years ago
    last modified: 2 years ago

    "dB(a) per 1,000 CFM" is not a single point measurement. It is quite literally a slope."

    You are confusing jr high school geometry with the real world.

    We do not have a slope or a line. We do not have data to produce a slope or a line or a curve or S-curve or knee or whatever. We have a few individual single points of data (that are far less accurate than we'd like but appearing much more accurate than I'd have hoped).

    -----

    Getting a bunch of data points and fitting a line to them would be great (if of limited or zero real world value) if this were lab data. This IS NOT lab data. This is not a controlled environment.

    OTOH, these are real world measurements of real world world range exhuast hoods in real world homes so in some sense are more valuable than lab data. By having people follow the same protocol as much as possible (using the same device (hopefully iphone 8 or newer), same app, standing in the same place facing the same direction, ...) we can hopefully reduce what variances/errors we can so that we can have fairly accurate comparisons.

    Going beyond this without better base data collected in a lab environment will only introduce potential for greater error and greater misunderstanding.

  • bry911
    2 years ago
    last modified: 2 years ago

    You labeled your table as dB(a) / 100 CFM. That is a slope! Here is a hint: "/" means "divided by."

    A point has an X and Y coordinate. Here is an example of a point... a Prizer hood produces 72 dB(a) at 100 CFM. The Y coordinate would be 72 dB(a) and the X coordinate would be 100 CFM.

    A slope has rise over run. Here is an example of a slope... a Prizer hood produces 72 dB(a) / 100 CFM. There is no given X or Y coordinate. There is the change in Y per change in X.

    Here is a middle school math problem using your chart. If a Prizer hood produces 72 dB(a) / 100 CFM, how many dB(a)'s would be produced at 800 CFM. The fact that anyone here can solve that problem means that you have a slope and not a point. If one did solve that problem they would arrive at the Prizer hood producing 576 decibels. Which is obviously wrong. (I realize that you made a typo in the chart, but that starts to become relevant as you denigrate my understanding of stats and data presentation). Just to be clear this is wrong in the real world, we all use slope in our lives.

    You are the one who drug this conversation over here. I was completely fine pointing out your error on another thread and going about my day. You have good intentions but that doesn't make you correct. Since you are the one who is accusing me of not understanding math and stats, let's take this to some math or stats boards over on reddit and see what they think.

  • vinmarks
    2 years ago

    "these are real world measurements of real world world range exhaust hoods in real world homes so in some sense are more valuable than lab data."


    Not really. You are putting a chart up that has no controls. If one hood is being measured with a silencer against another hood without a silencer then you are not comparing apples to apples. You have no models for the hoods just brands. Are these hoods 10 years old, 5 years old, the most recent models? Some are residential and some are commercial. It makes a difference.


    The chart is deceiving.

  • bry911
    2 years ago
    last modified: 2 years ago

    these are real world measurements of real world world range exhaust hoods in real world homes so in some sense are more valuable than lab data.

    As@vinmarks points out, this is not correct.

    There is a false dichotomy here. There are really just practical limits on the money that can be spent studying exhaust hoods.

    There are a lot of things that might cause a hood to be louder or quieter in a home. Researchers typically attempt to control for those things by removing their variability. A great "lab test," would be a series of actual hoods installed in the same way in an actual house. In that situation we don't need to worry about eliminating differences in installation because all the hoods were tested under the same conditions. Because it is impractical to install a series of hoods into the same home, these tests are often done on using some sort of quasi-installation that still hold the condition constant. Another option would be to take a lot of measurements from a lot of hoods installed a lot of different ways to arrive at an average for each and then compare.

    It is a fair criticism to note that quasi-installed hoods are different than installed hoods and that the results achieved in that test are different than they would be once installed. However, it is unfair to say that a test with a lot of uncontrolled variables is better than a test with controlled variables. You really don't, and can't, know that.

    This is not to say that examples of tests done in a few different installations doesn't have value. I am saying that you really want to be careful about manipulating that data. It is great to say that a particular hood achieved a particular result in a particular installation.

  • opaone
    Original Author
    2 years ago
    last modified: 2 years ago

    "Not really. You are putting a chart up that has no controls. If one hood is being measured with a silencer against another hood without a silencer then you are not comparing apples to apples. You have no models for the hoods just brands. Are these hoods 10 years old, 5 years old, the most recent models?"

    Evaluation of range exhaust hoods/systems is, by necessity, a system v system comparison, not a component v component comparison. Some are fully self-contained all-in-one units while others are component systems of hood, silencer, blower and controls as 4 separate components that are combined on-site.

    A silencer is not an option with an all-in-one unit, it is a common component on seperate component systems and is one of the advantages to choosing a component system with a remote blower. It would actually be deceiving to not include the silencer since that is one of the key benefits to choosing a component system.

    A lab test would actually not change things that much. The biggest difference would be knowing accurate CFM's given some specific duct/static-pressure systems - which would be quite helpful. A lab could have similar or identical SP's for each portion of the system and could vary these to show how they affect noise and CFM's. Components though would be the same with the only difference being that a lab test might provide a with and without silencer measurement for component systems.

    "Some are residential and some are commercial. It makes a difference."

    Yes. And no. If you read it that is a key point of the FAQ - that 'commercial' hoods all have large containment volume (and better designed baffles) and consumer, very stupidly, do not. But that is really the only significant difference - a bunch of empty space. Keep in mind that the hood itself is just a simple sheet metal box. That's it. My 'commercial' box is just taller than typical 'consumer' boxes.

    The only thing that makes mine 'commercial' and @kaseki's 'consumer' is who sells it. Wolf or Modernaire or Prizer or Prestige could easily sell a hood exactlly like mine in which case would that exact same box then be 'consumer'? I could just as well have paired my 'commercial' box with the same 'consumer' blower as @kaseki or any other. But @kaseki's blower is, I believe, actually the same as is used in commercial systems.

    In the end though, 'consumer' hood mfr's focus on marketing and taking advantage of the gullibility of American consumers rather than actual performance. So, if you want the quietest and best performing system then today you must buy a 'commercial' system.

    "The chart is deceiving."

    How so? The chart does a quite good job of showing what real world actual results people can expect from different options (and actually downplays how much quieter the Accurex, Modernaire and Wolf systems are).

    If someone installs the same Accurex system that I have in their home they can expect pretty much the same level of quietness depicted in the chart. If they install a VAH then they can expect the same noise as depicted in the chart. How is that deceiving?

  • bry911
    2 years ago
    last modified: 2 years ago

    How so? The chart does a quite good job of showing what real world actual results people can expect from different options

    The first chart (Range Hood Noise @ Highest Setting) does a somewhat good job of showing what real world actual results people can expect from Vent-A-Hood, and notes what a single installation of all the others were. That is all.

    The second chart is wrong, biased, and too likely to be misinterpreted even if it were correct.

    • It is wrong. It is not dB(a) / 100 CFM. If that were correct your quietest hood (the Accurex) which looks to be about 38 d(B)a/100 CFM would be 532 decibels @ 1400 CFM. Just for comparison Krakatoa's eruption, which is purported to be the loudest sound ever heard by humans, was only thought to be 310 decibels.
    • I realize it is a typo, but the fact that you posted this chart around for this long without realizing it was a typo goes a long way in demonstrating just how unreliable your assertions are. It was only after I did the math that you realized the mistake and then proceeded to claim I have "some surface level understanding" but I supposedly don't "have a good understanding of statistics or data presentation." You make a mistake that no data scientist and relatively few high schoolers would make and tell me I don't understand statistics.
    • It is also wrong because it is a slope and it assumes a linear slope. A fact that you already admitted in another thread but somehow forgot once you drug the thread over here. Just to be clear, I calculated the sones to decibels using it as a slope and got a ridiculous number which you admitted was too high. If I can use it as a slope in the conversion of sones to decibels in the calculation that discovered your mistake... it is a slope.
    • It is biased and likely to be misinterpreted because it assumes that sound efficiency of marginal CFM is always good. It really isn't. Here is the ELI5 version. In your first chart we see the third loudest hood is Wolf, but in the d(B)a / 100 chart we see it as the third quietest. That is because it produces more CFM at full power, but if you don't need 1,500 CFM then there is no benefit to a hood that is louder in daily use even if it is much more efficient. You are just adding useless capacity for a louder hood. You didn't provide measurements at lower CFM's and since you admit that it is not linear, you can't arrive at the sound level of Wolf at lower CFM's.
    • Where are other metrics. Where is the $ / dba chart?

    I honestly believe there is value in what you are doing. However, you consistently attempt to add impact to your analysis by manipulating the data and you consistently show why you shouldn't be doing that.

  • kaseki
    2 years ago

    My main blower is a Wolf sourced (but Broan manufactured) down-roof assembly not very dissimilar from the counterpart available from Abbaka. It may have imposed requirements different than the model Broan sells. My auxiliary blower is a baby down-blast blower sold originally by NuTone. Its style is commercial but flow rate is too low for most commercial purposes.

    In my mind, the physical difference between residential and commercial hoods is their setting height 2.5 - 3.0 ft vs. 4 ft above the cooktop, and their volume under the baffles for averaging transient plumes. More volume means greater hood height, although some of this can be achieved by larger hood entry area.

    @opaone how tall is your hood assembly? Residential hoods have to accommodate ceilings at 7 to 8 feet tall. This precludes Wolf etc. selling tall reservoir commercial style hoods into this market. (As one might imagine, a hood at 7 ft under an 8-ft ceiling won't have room for reservoir, baffles, and above-baffle volume for gathering the flow into the duct while keeping the flow even over the baffle space.

    Another factor that may be in play is that residential stainless steel hoods are expected to remain shiny and unstained. For this purpose, the higher-end manufacturers use 300 series CRES,* with its higher difficulty of fabrication and higher cost (includes chromium and nickel). Commercial hoods in many cases are stuck in kitchens hidden from the public, and they are fine using 400 series or similar CRES, which will stain over time but not corrode.

    Fancy residential kitchen hoods need perfect welds that won't discolor over time.

    (Is your hood magnetic? 400 series is, 300 series isn't.)

    ________

    *Corrosion resisting steel

  • vinmarks
    2 years ago

    How so? The chart does a quite good job of showing what real world actual results people can expect from different options


    What options? All you do is list a manufacturer name. You do not say what options each hood was installed with. You do not list model numbers. You do not list how old the hoods are. You can't compare a hood installed 15 years ago to one installed now because changes may have been made.


    If they install a VAH then they can expect the same noise as depicted in the chart.


    Really? Well which Ventahood models are depicted in the chart? Ductless, remote blower, baffle system etc?


    Kaseki has a Wolf hood that he says is quiet. I had a Wolf hood in my previous house which sounded like a freight train. Why the difference? They are both Wolf hoods correct?


    The charts lack a lot of information to be helpful. There are too many factors that go into how loud a hood is and it is not just based on brand. But according to your chart that is all the information we are given. A brand name.


    Maybe include all of what went into your accurex installation. Commercial custom made hood, silencer in the duct, proper isolation of blower and other components from the structure, makeup air, 18 inch duct size. Include model numbers for the hoods tested. Include how old they are, if silencers were used, are they remote blowers and if so where was the remote blower located, was proper duct size used. What other factors may have influenced how loud or quiet the hood was.

  • kaseki
    2 years ago

    "Kaseki has a Wolf hood that he says is quiet." Umm, better would be to say quiet enough to converse under with a normal speaking voice; it is not as quiet as a Miele dishwasher, next to which one can converse at a whisper.

  • vinmarks
    2 years ago

    @kaseki yes quiet enough. My Wolf was so loud. Forget about talking anywhere in the kitchen with it on.

  • kaseki
    2 years ago

    @vinmarks Did you have an external blower with a silencer in between?

  • vinmarks
    2 years ago

    @kaseki I had an external blower but no silencer. The blower was right on the outside wall which I am sure contributed to some of the noise.

  • kaseki
    2 years ago
    last modified: 2 years ago

    Thanks. Barely different than internal, in that case, unless an overpowered, under-operated blower was deliberately chosen to minimize noise.

  • opaone
    Original Author
    2 years ago

    "What options? All you do is list a manufacturer name. You do not say what options each hood was installed with. You do not list model numbers. You do not list how old the hoods are. You can't compare a hood installed 15 years ago to one installed now because changes may have been made."

    Agree. I thought I'd included this in the discussion but did not. I add what info I have. FWIW, the Accurex, Modernaire and Wolf are all external blowers w/ silencers. The VAH are all MagicLung.


    "The charts lack a lot of information to be helpful. There are too many factors that go into how loud a hood is and it is not just based on brand. But according to your chart that is all the information we are given. A brand name."

    Yes. In some cases though this is simply the best info that we have. I wish that we had better info but we don't.


    "Maybe include all of what went into your accurex installation. Commercial custom made hood, silencer..."

    This is a post that's been in the works for some time and I've simply not had the time to finish it. I think it is all covered in the thread but that's a gob of reading to find it. Hopefully soon.

  • opaone
    Original Author
    2 years ago

    "The blower was right on the outside wall which I am sure contributed to some of the noise."

    How much duct was there between your hood and blower? How many elbows of what degrees?

  • opaone
    Original Author
    2 years ago

    I added a details chart with what information I have.



  • kaseki
    last year

    Here are my measurements, better late than never I suppose.

    Hood system characteristics are given above and in other threads. Blower control is continuous type, so "medium" speed is not perfectly repeatable, whereas "slow" minimum and "fast" (maximum) are.

    Measurement is by Triplett SoniChek PRO 3550 with windscreen on. This device has a specified error of +/- 1.5dB. Operation was in "slow" mode (2 sec) and "A" weighting. Slow is not slow enough to average out whatever was slightly modulating the sound level, the the rough limits from eyeball observation are listed below. Mid value may be good enough given the base error.

    There are two sets of measurements, denoted "cook" and "tripod." "Cook" is hand held at my approximate ear level (~65 inches) standing at the cooking counter edge (roughly under the light bar of my Pro Island Wolf hood). "Tripod" was intended to meet @opaone's designated distances of this thread, but kitchen layout precluded achieving that exactly. Distance from sound sensor to inside of the light bar (edge of capture aperture) was 32 inches; distance from outside of hood depends on definition; height above floor was 5 ft, 9 inches. Note that this hood is wide enough that one is in the near sound field over over a range of positions along the hood length. This also means that 1/R^2 does not exactly apply if one were to try to scale to other perpendicular distances.

    Ambient varied apparently randomly between 30 and 37 dBA over numerous sequential sensor displayed readings. I couldn't hear obvious noises that were varying, so I can't explain it.



    The "Tripod" "slow" motor speed result is likely being modulated by whatever modulates the ambient, but it is possible to hear that the blower is on in this condition.

    opaone thanked kaseki
  • opaone
    Original Author
    last year

    Your hood is very quiet!


  • HU-479528764
    last year

    @opaone I would like to know if you have any general thoughts about the actual noise level of a range hood compared to its published noise level . I have recently bought two range hoods and been frustrated that the actual noose levels were MUCH higher than was claimed in their web sites and manuals. For one of them, the installer said ”thats’s just how it is.” Is that true? Do range hood manufacturers commonly publish misleading noise levels . My current range hood is a GE UVW9631 . They say the noise level on low fan speed is 1 sone which is about 28dB . The actual level for my range hood is 51dB . What is going on?


  • opaone
    Original Author
    last year
    last modified: last year

    Unlike the EU that requires specific measurements, the U.S. does not as far as I know. So manufacturers are free to measure however they want and obviously choose to show their product in the best light. My guess is that they measure in an anechoic chamber and measure with no ducting, short ducting and longer ducting and then publish whatever provides the lowest measurement.

    So yeah, pretty much worthless.

    Which is the point of this thread - to collect real data that provide real benefit to people.

    BTW, 1 sone is not necessarily 28dB. That sounds like marketing poop.

  • 2rickies
    last year

    @kaseki, I'm looking at the 42" Wolf chimney-style hood with an 1100cfm inline blower. The duct will go up to the attic and turn once to go out. There will be additional soundproofing in the ceiling above the kitchen. I asked about a silencer, and my architect said he's never needed to spec a silencer with this kind of setup. What do you think? Is the inline blower generally quiet enough?

  • HU-479528764
    last year

    @opaone Thanks for the reply . My recent google search says that there is a direct formula to convert sones to decibels . Maybe this will help some people:


    dB = 33.2×log10(Sones) + 28


    But for those a little less math oriented, there are conversion tables online. Of course, this formula does not help to tell you how loud a range hood will be based on published information since the published information is garbage . But at least it will help people prove that their range hood manufacturer is a liar . I did exactly that with a previous range hood and got a refund .


    So here are my data:


    Range hood make and model: GE UVW9631 professionally installed. Duct is about 1.5 meters long , right angle, externally exhausted , a reducer from 8” to 6” was required


    Ambient: 35 dB

    Low: 51 dB

    Medium: 60 dB

    High: 64 dB

    Boost: 67 dB

    Ambient: 35dB


    This is the published noise rating from GE (cfm/sones):


    100/1.0 (Working Speed)

    290/2.5 (Medium Speed)

    380/4.0 (High Speed)

    610/- (Boost Speed)


    For reference, the actual noise level of 51dB on low fan speed is about 5 sones , compared to the advertised 1 sone, 28dB. Way off.

  • kaseki
    last year

    @2rickies: Generally, compact high CFM blowers (versus, say, a Casablanca ceiling fan) have significant blade tip turbulence generated noise. This is best attenuated by having a silencer between the blower and the hood such as the silencers Fantech makes. Of course, you have to fit it into the space available, and they are 4-inches larger in diameter than the ducting. An external blower instead of an in-line blower may allow additional length if needed, particularly if angling the duct path towards a particular roof location.

    Suggest purchasing the connection clamps from Fantech to make installation easier.

    Note that noise goes as some power of the blade tip velocity, so another approach to quiet is to use an oversized blower and be able to operate at less than full speed when searing or wok cooking.

    https://shop.fantech.net/en-US/silencers/c115516

    https://shop.fantech.net/en-US/mounting--equipment/c115517

  • 2rickies
    last year

    Thank you @kaseki, this is very helpful. I think/hope the blower I'm planning is larger than what I'll need, so I'm hoping I can use it on lower settings. I'll have a 36" induction cooktop, vs the pro gas range I have right now, so at least I won't have to clear burning propane.

  • kaseki
    last year

    For 'quiet' cooking, induction will result in a lower plume velocity as well as plume volumetric flow rate, but that isn't the condition that needs to be dealt with. Searing meat, wok cooking, etc., will lead to large transient plumes, and for this one needs high CFM and/or a large volume under the baffles to average out the plume across them. This latter capability is typically only available from commercial hoods.

    Some here have gone quasi commercial (see https://bamasotan.us/range-exhaust-hood-faq/) with varying volume under the baffles for just this reason.

  • 2rickies
    last year

    @kaseki, I see. The KD is bent on finding a modern (flat rather than pyramid) hood, and I'm insisting on angled baffles...They priced hoods from modernaire that met both of those requirements, but they were out of my budget range. I've been focused on the chimney style with angled baffles that seems readily available for residential customers and in my price range. The bulky appearance of a commercial hood is also an issue, because it will be against a wall with no cabinets above it and it needs a chimney extension for a 13-ft ceiling. It's at one end of a great room, so very visible from everywhere.


    I'm wondering about something you said about silencers--how is it they're too large for the ducts? I see fantechs that are made for 10" ducts, which would be the size i need. I must be misunderstanding something. And would a silencer cut down on the potential cfms? Or does it have no effect on that?

  • kaseki
    last year

    The silencers are not too large for the ducts, but they may be too large for the space available. I have a 10-inch duct from my hood to my roof blower. If you were in my attic and could see the amount of bulk that represents, including the silencer section that is 14 inches in diameter, the hangers, and the dampening material I used on the duct sheet metal, you might wonder how someone could try to stick the duct and silencer in a wall cavity, or some other compact area. (I think @opaone built an internal chase in his house for his ducts.)

    I also have an 8-inch duct with silencer going to the roof where a down-blast NuTone blower is mounted. This adds a bit more volume fill.

    There is very low pressure loss in the Fantech silencers, probably nearly the same as the equivalent length of duct by itself. I once got a number from Fantech but would have to hunt for a while to find it. The interior of the silencer is the diameter of the duct, with little holes entering the outer volume (that is filled with some dampening material, I suspect).


  • 2rickies
    last year

    @kaseki thank you for clarifying. I should have plenty of room in the attic where the duct will run, and I'm going to add a Fantech to my plan.

    I read @opaone's guide--very helpful. I noticed a recommendation there for a Prestige canopy-style hood as being better than most noncommercial hoods in terms of containment area, etc. I looked at their classic chimney hood (unfortunately I can't use a canopy hood), and it also seems better designed than the one I was considering. I like that the lights are in the center, and not in the front. It should cover the front burners better as a result.

  • opaone
    Original Author
    last year
    last modified: last year

    I think sones to dB is a bit more complicated. Partially because a simple calc like that doesn't account for frequencies which is why I was hesitiant to include a sones chart.

    In the end the best vehicle for accurate comparison is I think using dB(a) and taken 1m in front of the hood at a height of 1.75m.

  • 2rickies
    last year

    Oh well, looks like I can't use an inline blower with that Prestige pyramid classic hood, so i'm back to the Wolf or something else... It would be simple if I could just go with a canopy hood.