I Want Your Honest Opinion, What would U Do?

udarrell_2007
14 years ago

1 1/2 ton Heil with 2-ton evaporator coil. A TXV Metering device.

Extremely low indoor airflow, I would estimate airflow at only 375-cfm, or 250-cfm per-ton of cooling.

Subcooling is only 1-F.

Gurgling sound in evaporator area.

What could be causing that?

Condenser discharge air temp/split is only 12-F above outdoor temp.

TH set at 78-F Runs all the time even in mild weather.

Tech never said indoor airflow was too low.

A so-called tech came out & only checked the suction pressure & said the charge is okay. User, believes the installing company.

What do you say?

What would you do to correct the apparent problems?