srseverance

Yet another hood, CFM, and MUA question

srseverance
6 years ago

We are in the beginning stages of planning a kitchen
remodel. I am hoping, after the remodel, to be able to cook under a truly adequate
hood for the first time.

The range will be a thirty-inch-wide standalone or slide in
either electric or induction. Our cooking runs the gamut. What I think will
stress a ventilation system that we do is searing steaks, stir-fry’s, and cooking
pasta. Getting the grease and humidity out of the kitchen would be nice.

Our current thinking has the range against an interior wall.
The hood will be wall mount, exhausting upwards. The duct will either be
straight up through the attic out the roof. Or the duct will enter the attic,
take two obtuse angles and out the roof.

Distance from stove top to hood has not been decided yet.

CFM

I have read some of Kaseki’s comments. If I understand the
recommendations I would want a hood 36 inches wide by 27 inches deep, with a
flow rate of 90 CFM per square foot of “hood aperture.” To get that flow rate
Kaseki recommends a blower rated for 50% more. (135 CFM/SF)

What is “hood aperture”? Is it the 36 inch by 27 inch
opening at the bottom of the hood?

Assuming the aperture is the wide opening at the bottom of
the hood, using the above recommendations:

3 feet * 2.25 feet * 135 CFM/SF = 7.5 SF * 135 CFM/SF =
1,012.5 CFM

Call it 1000 CFM.

From a position of ignorance this seems grossly inflated.

The questions:

  • What CFM range will work well?
  • Who makes a 27-inch-deep hoods, besides Wolf? Or how does
    one get 27” deep coverage to catch the fumes coming off the searing steak in
    front?
  • Any hints on how to research local make up air requirements?
    (Local in this case is Renton, WA.)
  • And is there any way to preview before posting on gardenweb?