Makeup air unit and dilemma with a range hood
Comments (5)I'll second (third?) the recommendation to check the Appliances forum. Having read quite a bit there on this subject (with a special eye to Kaseki's posts), in addition to the stated CFM on the fan, you also need to consider the size of the duct to the exterior (bigger diameter = better airflow) and the turns in it (more turns slow down the air), the height of the hood above the stove top (closer = better) and the capture area of the hood. It's a complicated subject, one that was partially thwarted by my DH who complained mightily that the hood was stupidly low. Sigh . . ....See MoreNeed advice for a make-up air system for vent hood
Comments (10)First, this is what the proper calculations would say about Risinger's installation. OR THIS Second, short circuiting a hood, air curtains, and generally any makeup air introduced too close to the range will produce counterproductive turbulence that will reduce the effectiveness of the hood to the point that he may as well have just put in a 400 CFM fan without makeup air. Third, the floor under the range is required to be sealed from drafts on most ranges. But, you can't usually shove ALL that air through the HVAC system either...See MoreVent hood question - make-up air turbulence, acceptable neg pressure?
Comments (3)Adam with that much CFM on the blower, if you stand to close you might get sucked out hahaha, only joking.One question did they use the right size ducting material that the manufacture recommend if undersized this could be the source of your problem....See MoreVent hood question - make-up air turbulence, acceptable neg pressure?
Comments (13)This is an issue that requires some measurements and some analysis. To even know where you are you need to measure the pressure in the house relative to outside the house as a function of different settings of vent air flow and MUA air flow. Either hire someone to make the measurements or buy (cost is fairly modest, as I recall) a differential air pressure device. In test kitchens, the means of introducing MUA is via a perforated wall some distance from the test stove/vent air handling equipment (hood). What is desirable is that the MUA, when it gets to the air volume between the cooktop and the hood entry aperture, be relatively non-turbulent. Introducing MUA at one's feet next to the stove may or may not achieve this. Often the toe kick spaces there are too small, and may, depending on configuration, aim at some other structure (wall, island, whatever) that will force the air flow up. Now there is turbulent air all around the cook and the hood. I think the MUA exit area(s) should not be too much smaller than the hood entrance area unless the MUA injection point is fairly far from the hood. In a (completely burger odor free) burger joint in Concord NH there is a CaptiveAire system in which the MUA is expelled downward from the ceiling in front of the hood. (This aperture is actually part of the hood assembly.) I would estimate that the MUA aperture is roughly half that of the typical very large commercial hood aperture, although I cannot see all of the hood aperture from the customer seating area to be very exact about this. In my residential configuration, a 3 x 3 foot ceiling diffuser is used about 20 ft down a hall from my 10 sq. ft. aperture hood. This hall delivery should slow down the air velocity to about 37 ft/min, which is a slight breeze -- less than a half mph. I haven't pressurized the MUA yet, but I have seen the effect of an interior split cycle air conditioner head spilling air toward the hood, there is significant plume displacement. Is your MUA source via a basement, or via the roof? It might be better if you dumped the MUA at the ceiling directed away from the hood such that the air takes a longer path to the hood aperture. Or dump it into diffusers at various locations in ceilings connected to the kitchen. (This might be a casus belli if not heated.) Or use a lot more toe kick area. Besides measurement, I would check that with windows open, MUA off, and hood on, that you can cook something and see it fully captured and contained by the hood system. Then as you close up windows, and do whatever you are doing (manually?) to set MUA flow, does this start interrupting the capture efficiency? And yes, if you don't have a closed loop controller then both hood and MUA should have continuously variable controls. By analysis I meant making a gross estimation from the hood system fan curve and the properties of your vent system of what flow rate you may be achieving. (There are contractors who can measure this by temporarily replacing a door with a measurement device.) Ditto for the MUA system. What is its fan curve vs. ducting, filtering, diffuser pressure loss, and heating scheme, if present? If your actual replacement air is 200 CFM, then ideally you want the MUA to be 200 CFM less than the hood can pull when the house pressure relative to outside is zero. One expects that if the house pressure is positive, more air will flow out the hood system. But in your case I suspect, as did opaone above, that there is really a lot of turbulence around the hood and this turbulence is interfering with the cooking plumes attempting to rise to the capture area (the hood entry aperture). kas...See MoreHU-109832731
2 years agoHU-109832731
2 years agolast modified: 2 years agoHU-109832731
2 years agokaseki
2 years agoM
2 years agoHU-109832731
last yearkaseki
last yearUser
last yearlast modified: last yearHU-109832731
last yearHU-109832731
last yearUser
last yearlast modified: last yearHU-109832731
last yearM
last yearlast modified: last yearHU-109832731
last yearUser
last yearHU-109832731
last yearlast modified: last yearHU-109832731
last yearkaseki
last year
Related Stories
KITCHEN DESIGNHow to Choose the Right Hood Fan for Your Kitchen
Keep your kitchen clean and your home's air fresh by understanding all the options for ventilating via a hood fan
Full Story5 Stunning Modern Range Hoods
Today's kitchen range hoods can look like sleek sculptures. Here's what to look for when you go shopping for one
Full StoryKITCHEN APPLIANCESDisappearing Range Hoods: A New Trend?
Concealed exhaust fans cut visual clutter in the kitchen
Full StoryKITCHEN DESIGNHow to Get Your Range Hood Right
Get a handle on the technical specs, and then learn about fun design options for creating a beautiful kitchen feature
Full StoryKITCHEN APPLIANCESWhat to Consider When Adding a Range Hood
Get to know the types, styles and why you may want to skip a hood altogether
Full StoryKITCHEN DESIGNWhat to Know When Choosing a Range Hood
Find out the types of kitchen range hoods available and the options for customized units
Full StoryKITCHEN DESIGNDesigner Tips for Range Hoods, Appliances and Lighting
Learn how to get your microwave height just right, what kind of bar stool will be most comfortable and more
Full StoryKITCHEN DESIGNA Cook’s 6 Tips for Buying Kitchen Appliances
An avid home chef answers tricky questions about choosing the right oven, stovetop, vent hood and more
Full StoryKITCHEN APPLIANCESLove to Cook? You Need a Fan. Find the Right Kind for You
Don't send budget dollars up in smoke when you need new kitchen ventilation. Here are 9 top types to consider
Full StoryMATERIALSInsulation Basics: What to Know About Spray Foam
Learn what exactly spray foam is, the pros and cons of using it and why you shouldn’t mess around with installation
Full Story
User