tuften

live wire with circuit off

tuften
9 years ago

Have a 1929 cape with steam heat and bx cable behind plaster
and lath walls.Decided to replace an outlet right behind the cast
iron radiator because it wasn't holding the plugged in wires any
more from years of heat.The outlet is feed power from a jbox just
below in the cellar and is the first outlet from the fuse #4.After killing the power to the outlet and disconnecting its leads from the
fuse I found that the duplex still had power. 120v neutral to grd,
120v hot to grd but 0v neutral to hot.I then shut off all the other
fuses one at a time until the duplex had no power.This happened
when fuse#5 was tripped.I then tried to figure what on fuse#5
could be feeding power to fuse#4 when I remembered we had our kitchen redone 5 yrs ago by an electrican and at that time
the kitchen light was on fuse#4.He remodeled the lighting to 4
ceiling recessed lights and 2 under cabinet lights and put them all on fuse#5.I traced his wiring to a small screw in type fuse subpanel in the cellar ,this subpanel got its power from
fuse#5 at the main.When I pulled the wires for the kitchen lighting from this subpanel I had no more voltage back feeding(if correct) to the dulpex on fuse#4.What do you think
the problem is here,did he some how tap into the other circuit
without knowing.Its been 6yrs wired like this and we have had
no electrical issues at all come up.Your thoughts are greatly appreciated