Help choosing Heat Pump in Florida – Load Calc from Online Source

User
8 years ago

I have a small 60 year old beach house. My current installation is a 14 year old 2 ton
12 SEER Rheem that no longer functions.
I have had the same 2 ton capacity for the last 25 years. All the contractors are trying to move me up
to more expensive 2.5 ton. It’s a small
job and I’m having problems getting load calculations from the contractors. I got
an email response from one saying the calculations suggest a 2.3 ton, but no
actual documents. I do know that when talking
to the estimator about a load calculation, I found out his software had no
provision to account for things like a 6’ wide canopy over most of my south
facing windows. I tried the online load
calculator, but I’m not sure I’m getting even close to a correct measurements.

The literature on most of the 2.5 ton units suggest they
will get 1% -2% loss due to the current size of my line set being 5/8 instead
of the 3/4 recommended for the 2.5 ton units.
No contractor has suggested changing the line set, but I understand that
can be expensive and wonder if it is necessary to do the job properly? Is this
something to consider and will it affect the performance of the unit over time?

I have some space constraints as the air handler is in an
old furnace closet and a larger unit may need to have some extra access
installed. One Bryant dealer told me I
needed to install a pump because of the space available and the size of the 2.5
ton unit. I’ve never had a pump before,
but I do know the sound is irritating and the closet is near the living room.

I also wonder about noise as the fan on the 2.5 tons seem to
operate at almost 50% more RPM’s than the 2 ton.

I don’t like going high end on HVAC because I don’t think I
get a return, I’m satisfied with a 14 SEER, 11.5 EER. I think that’s all I
need. Things don’t last too long in this
environment and after about 10 years it seems that the efficiency really starts
to decline. Even more expensive units
seem to suffer. My understanding is that true variable speed units (sorry if
the nomenclature is incorrect) are available in high end units and should be
the norm by the time this unit needs to be replaced in about 10 years. I would like to install a 14 SEER, 11.5 EER
with a 5kW Heat Strip (30 Amp Circuit) in 2 ton now and spend the money on the
next install when the tech catches up.

I’d like to know if you think my estimate of replacing the
A/C every 10 years in this environment is reasonable, if you think I should
stay with a 2 ton or move up to a 2.5 ton, if I do replace the units about
every 10 years if staying at the less expensive range of installations is more
practical and some recommendation on equipment (14 SEER, 11.5 EER with a 5kW
Heat Strip (30 Amp Circuit). I know the
installer is critical, but some of the best ones seem to use ICP products for
their less expensive installs, do any of you have any thoughts on those
products?

These are the results I got from the online load
program. That program didn’t have a
provision for block walls (I used brick with no insulation) and had no
adjustment for shading on the south wall.

I used, Brick with no insulation, Concrete Block on Slab, 1,150
as the conditioned square feet, 9,250 for cubic feet, Average Construction,
Attic Ductwork with R-6 insulation and Good for duct tightness. The paperwork for the ductwork doesn’t have
an R Value, so I used R-6 as it was only two years old. I used good for duct tightness even though
when a previous duct system was tested I was told the building was almost too
tight. I could not adjust the shading to
represent the canopy on most of the south exposure. All of the glass is Low-E with blinds, vinyl
clad, Miami-Dade hurricane rated. I have
two doors with dual pane inserts, one facing north and one south under the
canopy. The canopy is 6 feet wide and
covers all but one of the south facing windows.

Total BTU’s Cooling:
18,266

Sensible Load: 16,075

Latent Load: 2,191

Total BTU’s Heating:
15,408

Thanks to Gary for Providing the online load calculator at http://www.loadcalc.net/