sub panel question

16 years ago

What is the largest sub panel you can run off of a 100 amp main? My main is 24 circuit and I am out of space. Ideally i would have about 16 more circuits. The amperage is not a problem just the number of circuits. I would like to avoid changing the whole panel as this would require removing the meter and I don't want to do that.

Comments (26)

  • 16 years ago

    Not sure I understand your need for 40 circuits especially with 100 amp service. Another option would be to replace large breakers with double slims which give you two breakers in the space taken up by one. What brand of panel do you have? It sounds like you are really in need of 200 amp service. What's the problem with pulling a meter?

  • 16 years ago

    You can run any size sub you want. The limit would be the feeder, which is 100A, but you could even run a 200A sub if you want, as long as the feeder is 100A or less so that you don't trip the main disconnect.

  • Related Discussions

    Basement Sub-panel

    Q

    Comments (6)
    You do not add up the individual breakers to come up with the main breaker. 60 should be plenty. I have a 100a service on a 20 slot main box that feeds 350a to 400a if you add up all the individual breakers. In daily life you never use all that power at once.
    ...See More

    Yet another sub-panel question

    Q

    Comments (11)
    Saw this post elsewhere: "At the shed panel you need to have the neutral bar and all neutral wiring together isolated from the grounds. The ground needs to all be on one bar and attached to the panels metal enclosure. Only back at the first means of disconnect ( where the main breaker for the house is located) do the ground conductor and neutral conductor tie electricaly and physically together. You don't have to have a ground rod at the shed. But it dosen't hurt. It should only be tied to the ground bar not the neutral bar. Should a lighting strick hit the ground or shed it will look for the shortest path. And a extra ground rod will help in that situtation. If your neutrals and grounds are made up correctly then they are electrically tie together thats what keeps them at the same potential. It's when telephone and cable tv companies drive their own rod and do not tie or use the service ground is when you have problems. But you did the correct thing you ran a 4 wire feed to your shed. And by doing that grounds and neutrals are kept seperate."
    ...See More

    Wiring a sub-panel for Aux. generator

    Q

    Comments (6)
    I was looking at wiring diagrams for prewired transfer switches and they do exactly what I want to do. Take the hot wire off the breaker and connect it to the transfer switch which contains a breaker but they leave the neutrals and grounds where they were. So are they also wrong? I am not aware of the derating current when using a conduit but I suppose it has to do with "back emf" or eddy currents. I will have less than 15 feet of conduit and thought it easier & neater than running 12 NM cables. However I can just run 12 black(hot), 12 white(neutral) & 12 green (ground) in my 1 1/4 conduit. Or are you suggesting 3 separate conduits for each type of run?
    ...See More

    Sub Panel Question

    Q

    Comments (4)
    Given the loads you describe, you should be well within the capacity of a 50-amp sub-panel and still have room (and ampacity) for another circuit or two. This assumes that the electrician wired the panel with a 120/240V feed, which would be the usual practice. (It's a two-pole or "double" 50-amp breaker in your main panel, right? Also, the use of the 12/3 doesn't make any sense unless the panel has a two-pole feed.) That being the case, keep in mind that each of the two legs provides 50 amps of current at 120V. If you have no 240V loads, you can think of that as like having two 50-amp feeds, or 100 amps of available power for 120V circuits. IMHO, you'd be better off running a new circuit for additional receptacles than tapping the warmer drawer circuit because, technically speaking, there's a potential code violation lurking when you don't follow the manufacturer's specifications for a dedicated circuit.
    ...See More
  • 16 years ago

    The main panel is full as the original owner ran very few things on each circuit. Now I am redoing a kitchen and this requires many new circuits.

    The wire coming into the main panel are very short and to replace the panel I would have to replavc the wire to the meter. Half of the meter is live correct? Just would like to avoid this.

    The panel i have now is an older one and breakers are very expensive for it. Double slims are not even available for this. I think it is a commander

  • 16 years ago

    "Now I am redoing a kitchen and this requires many new circuits."

    I assume those new cc'ts will be 20A for countertops, maybe a dishwasher, garbage disposal, microwave, etc. I'd suggest the same thing as Texas, bite the bullet, put in a 200A service, and a 40 slot panel. That way you can recombine many of those small individual cc'ts into single 15A or 20A cc'ts (depending on wire guage) and have lots of future kitchen options. If you're doing this yourself and are hesitant, you could hire a licensed electrical contractor to do the service entrance and panel upgrade, and you do the rest.

  • 16 years ago

    Not sure I understand all I know about the subject, but Commander is related to Cutler-Hammer. CH breakers are available at Home Depot. CH1515 and CH2020 are slim double breakers. It could be that Commander is the Canadian version of Cutler-Hammer. I believe the large bird is the Canadian expert.

  • 16 years ago

    Good info from everyone.

    Clax66: I had a 2650 sq ft house with full basement that had 100 amp main service, and we never tripped any breakers. It had all gas major appliances.

    The number 1 thing you should do is do a proper load calculation as terribletom said. Base your decisions on data, not opinions. If with the kitchen appliance additional loads you are still under 100 amps calculated total load, fine. I'm not an electrician, but I've done a lot of electrical work to various houses, and my understanding is you can put a 40 circuit subpanel in if you want, as long as you don't exceed a total calculated 100 amp load.

    So, you can have a subpanel fed from a 100 amp breaker, in your 100 amp old panel. The subpanel can be any size number of circuits, as long as it's rated for the breaker that's feeding it. Some small subpanels only have a 70 amp rating. Most seem to be 100-125 that I've seen.

    Do the load calculations. Then if your main service is adequate, you can install a 40 circuit subpanel fed by a 100 amp breaker, as long as your TOTAL calculated load is under 100 amps.

  • 16 years ago

    Here you go:

    Here is a link that might be useful: Commander---> Cutler-Hammer

  • 16 years ago

    I would be surprised if you have a 100A panel, look at the nameplate. If you main breaker is below several 220 breakers you have a much larger box. The rule as I understand it is it doesn't matter what size sub-panel you use. You can use a 200 amp sub panel and feed it with a 30 amp feed if you like. Just size the breaker appropriately for the wire size you use to feed the panel. I have over 50 breakers in my home and the major appliances are gas same as you. I think I have about 20 breakers feeding the benches in my basement. I ran 12X3 W/G and split it into two 20 amp circuits which I then ran around the bench. I used GFCI breakers as the initial duplexes and regular duplexes thereafter on each circuit. If the neutral breaks the GFCIs will open so no chance of 220V in anything. My total basement load is normally about 15 amps but I can plug in a compressor or whatever I like without worry. One person suggested using Tandon breakers (never herd of slims). You need to do some de-rating if you put more then four of them in a panel. No one could tell me how but I just fed 100A branch panels with 60 amp breakers and the inspector had no problems.

  • 16 years ago

    It is "tandem", NOT the name Tandon. Tandem as in side by side. Another name is twin breakers. Slim is common name for GE style breaker that are not connected, they are simply 1/2" wide as opposed to the typical 1".

    NO, you DO NOT have to derate when using twins. You DO have to make sure your panel will accept them. THIS is the key.
    Not all panels will accept twins, tandems, skinnys, etc.

    The reason you can feed a panel with a larger breaker is because the panels are rated in large gaps of sizes. Wire and breakers are more definite. It is completely typical to feed a 125A "rated" sub-panel with a 50, 60, 70, or 90 amp breaker.
    Besides, the code tells us we can do this. I can find it if you want.

    Gil, are you an electrician?

  • 16 years ago

    Sorry my speller changed that one, you are correct it is tandem.

    I got my journeyman card in about 1960 from the local IBEW, but I do not see that as any requirement to answer the questions posted here. I also have my electrical and electronic engineering as well.

    What is your background?

    I made the change to electronics in about 1972. Is my journeyman still valid probably not, don't matter to me.

    You might look into the NEC or other code. The local code states no more then 4 tandem breakers unless the box is de-rated, I think I saw that in the NEC, not sure.

    Consequently, as stated above, you were mechanically forced to limit the number tandem breakers in a panel, Currently I am not sure if that still holds true.

    I asked the local inspector if feeding a 100A sub panel with a 60 amp breaker, he said that would suffice.

  • 16 years ago

    "I got my journeyman card in about 1960 from the local IBEW, but I do not see that as any requirement to answer the questions posted here."

    No, but having a GOOD clue about CONSTRUCTION and BUILDING electric, and a strong knowledge of the NEC ARE mandatory.
    This is not written anywhere but those of us who are versed in this do keep incorrect or erroneous replies in check.

    "The local code states no more then 4 tandem breakers unless the box is de-rated, I think I saw that in the NEC, not sure."

    That's fine for your local code, just don't post that information as fact. STATE that it is YOUR local code.
    NO, it is NO in the NEC.

  • 15 years ago

    I'm feeding a 125amp sub panel from a 100amp main panel with 6g wire and a 50amp breaker is this ok? I have 3 wires going to the sub panel 2 hot and one ground. I have a neutral bar in the sub panel, but no ground bar, does the ground hook into the neutral bar or should I buy a ground bar and put it in the panel?

  • 15 years ago

    #6 wire being fed from a 50A double pole breaker is fine. You need a neutral (white) wire feeding your subpanel if any circuits will be 120V. You need to separate the grounds and neutrals in the subpanel, so yes, you need to buy a ground bar.

  • 15 years ago

    ... and run a ground wire.

  • 15 years ago

    If there are a lot of small branch circuits you can do a load calculation and probably join some of them into a single branch circuit and free up space that way.

    The slim/double/tandem breakers and the boxes they fit are designed to prevent more than 42 devices in a panel since that is the limit.

    If the panel is old enough it may not be listed for use with the smaller breakers.

  • 15 years ago

    "... and run a ground wire."

    OP already stated she had 2 hots and a ground.

  • 11 years ago

    I know this thread this old but here I go...If you only have 24 circuits in your panel you should swap your panel for one with 36 circuits homedepot has them with the main 100amp breaker and 6 free 20amp breakers for under $60..the line to the meter is called the kick which in not hard to replace and when the meter is pulled off the kick is no longer live..to run the sub-panel you can only use 25 percent of the breakes that are in your main panel so 25 percent of 24 would be the amount of circuits you can put in the sub-panel..and if you also do the math you can only use 80% of the amps on your 100 breaker..you can not take it to 100%..only in lighting can you you 100 percent of the breaker..and yes you must have the neutrals and grounds on separate bars only one neutral to a lug and up to 2 ground to a lug..to try and swap all that around it better just to swap the panel for one that has more circuits..if you feel uneasy about doing that then your better off paying a licensed electrician to do it for you...cause you don't want to try and save a buck and burn down your house or hurt yourself

  • 11 years ago

    "original owner ran very few things on each circuit"

    Why not just map out the existing breakers and see how many can be pigtailed together onto a single breaker.

    If the loads are low on the existing circuits you should be able to free up enough slots for your kitchen remodel.

  • 11 years ago

    As long as you don't have to do other things like install AFCI's which I've never seen tandems/skinnies to do.

  • 11 years ago

    "OP already stated she had 2 hots and a ground."

    He needs two hots, a ground, AND a neutral if he wants 120/240 V.

    Ground and neutral are NOT the same or interconnected except in a main panel or in older range and dryer circuits.

  • 11 years ago

    This thread is from 4 years ago.

  • 11 years ago

    "I know this thread this old but here I go...If you only have 24 circuits in your panel you should swap your panel for one with 36 circuits homedepot has them with the main 100amp breaker and 6 free 20amp breakers for under $60..the line to the meter is called the kick which in not hard to replace and when the meter is pulled off the kick is no longer live..to run the sub-panel you can only use 25 percent of the breakes that are in your main panel so 25 percent of 24 would be the amount of circuits you can put in the sub-panel..and if you also do the math you can only use 80% of the amps on your 100 breaker..you can not take it to 100%..only in lighting can you you 100 percent of the breaker..and yes you must have the neutrals and grounds on separate bars only one neutral to a lug and up to 2 ground to a lug..to try and swap all that around it better just to swap the panel for one that has more circuits..if you feel uneasy about doing that then your better off paying a licensed electrician to do it for you...cause you don't want to try and save a buck and burn down your house or hurt yourself"

    WHY would you dig up a four year old thread to post a bunch of INCORRECT gibberish????

  • 3 years ago

    First of all the gentleman needs to have a licensed electrician or the city electrical.inspector come and look at what your wanting to do. Many times people may have helped someone install some wiring or new receptacles or replace a switch this doesn't make you an electrician..Once the expert has looked at your project they can usually tell you the right way to accomodate these changes. There are rules that are changing every four years for each new code book. Each change is generally made because a situation occured where someone was electrecuted or died as a result of the cicumstances. Second there are certain requirements for certain appliances , special.use outlets, and the overcurrent protection required. And the bonding not grounding of the subpanel.is very important. EVERYTHINGS FINE UNTIL YOU JACKLEG SOMETHING TOGETHER IN YOUR HOUSE AND CONSEQUENTLY IT BURNS DOWN OR SOMEONE GETS HURT OR KILLED. This isn't a common occurance but its always in the realm.of possibilities. Is that a risk your willing to take to save a few.bucks..I am journeyman electrician been one for 35 years and iv'e seen it all. The best advice is to get an expert opinion and get a permit so the new work will have been signed off by someone. This is very handy if your house does burn down or someone gets hurt cause that can happen no matter what..Insurance companies tend to avoid paying for moonlight work done by the home owner and his buddies after a twelvepack one sunday afternoon.


  • 3 years ago

    My point is being made if you read the post right before mine this guy has no idea or has a little bit of knowledge but nothing he's saying makes sense. If you want to know how to do a load calculation properly go to the library look it up in a new code book. THE EASIEST WAY IS TO USE THE ALTERNATE METHOD OPTION THEY GIVE YOU AFTER THE FIRST LOAD CALCULATION IS EXAMPLED AND EXPLAINED. AGAIN HIRE OR ASK SOMEONE WHO KNOWS WHAT THEY ARE DOING.

  • 3 years ago

    I'm going to jump into this rabbit hole by relating my, ultimately positive experiences. When I bought my Long Island 1895 house, its original electrical service was 30A 110V panel with 4 15A fuses to a small number of circuits. It had been replaced with a 60A, 240V service (again with fuses) and several more circuits run, including one for an electric clothes dryer, a hot water heater, and a room air conditioner (the only circuit with Romex).


    Like the OP, I decided I needed more circuits, and would prefer a breaker box rather than a fuse box. I investigated having a new service run with new meter and put in a 200A breaker box myself but the restrictions were so great, I gave up on that idea. I would have had the POCO come and pull the breaker (a 2 week wait for that service), the install my new meter pan and panel, have it inspected (another 2-4 week wait), then have the POCO put in the new meter. I couldn't deal with all those delays, so I decided to go the "subpanel" route: I purchased a 40 slot load center and mounted it next to the old fuse box. I then ran 4 Ga wires from the old fuse box to the new breaker box and started moving circuits. When I had finished moving all the old circuits, I essentially abandoned the old box, using only the 60A cartridge fuses as primary protection. Finally I called a licensed electrician come in and replace the meter pan, meter, and reconnect the new panel. It took him about 2 hours to accomplish all that.


    While I was operating my new panel from the old 60A service, I never blew the main breaker. But that's understandable, since I had essentially no high current appliances, especially after I replaced my clothes dryer and domestic hot water heater with gas appliances. So I accomplished my original goal: more breakers to run more services, but not use significantly more power.


    On a side note, there was only one 15A circuit for the entire second floor; that must have been left over from the original wiring. Very difficult to run new wiring from the basement to the second floor, so I managed to run 3/4" EMT from the basement to the third floor (attic) and put in a 50A subpanel there, and run all the necessary lighting and receptacle circuits circuits from it.


    End of rabbit hole!