SHOP PRODUCTS
Houzz Logo Print
carpediem12_gw

Carrier 96 or American Standard 97 or Carrier 92?

Carpediem12
9 years ago

In a prior post (Which of these two Carrier gas furnace and A/C systems? Posted on 8/18), this system was the preferred one due to better dehumidification:

Proposal #1:

AC 24ANB 636 16 SEER/13 EER � 3 ton AC
Furnace 59TN6AO80V17-14 96% 2 stage ECM � 80,000 BTUs
Coil CNPUP3717ALA
Thermostat Infinity Touch (WiFi)

Net cost to me after various rebates and discounts: $7,928

A second contractor has proposed this system:

Furnace American Standard model AUH2B080A9V3, 2 stage variable speed (American Standard Gold ZM-80,000 Btu�s, 97%)

AC American Standard model 4A7A6030H1, single stage (American Standard Gold XI- 15 SEER 2.5 ton)

Coil American Standard model 4TXCB036BC3

Thermostat American Standard digital programmable

Net cost to me after rebate: $6,285

Which is the preferred system? Why the difference in AC size 2.5 v 3 tons? It is hot and humid here in the summer but I have a 2.5 ton AC currently. I think Manual J might say 3 tons? Will that be more costly to run on my electric bill?

And finally, a third contractor besides quoting a price on a very efficient system (Carrier 98% - cost to me $8,465), also priced this one:

Carrier Brand Comfort 92 Single Stage Gas Furnace model #:59SC2060S17-16 with a 60,000 Btu input capacity and a 56,000 Btu heat output capacity and a PSC blower motor

Carrier Comfort 13 series outdoor air conditioning condensing unit model #: 24ABB336W003 with a 3.0 ton cooling capacity

Comfort 13 all aluminum N series vertical evaporator coil with insulated jacket model #:CNVP4217ALA with a 3.5 ton cooling capacity

Carrier programmable thermostat model #:TCPAC01

Cost to me: $4,300

This price is for a 60,000 BTU furnace � not 80,000 � why the difference in BTU�s? I hated the heat pump I got rid of in 1996. I had big utility bills AND was cold. I do not want to be cold. I think my current furnace is an 80,000 BTU furnace.

In discussing the project with contractor #3, he asked if I was happy with what I have and I told him if the furnace didn�t have a crack in the heat exchanger, we would not be having this discussion. What I currently have is a Carrier gas furnace 58 MXA 080-01-12 92% AFUE, a Carrier AC 2.5 ton 13 SEER, 38 TRA 030-3, Advanced Products coil with time delay HA 10436-175, and a programmable thermostat. And I am happy with it.

While I can afford any of the options, it seems to me since I use about 500 therms (heat and cook top only � gas is .50/therm here) and 20,000 kWh annually (AC and hot water and everything else � 8.8 cents/kWh), the price difference ($3,628) to gain 4% extra efficiency in a furnace (is that really $10 � 500 times .5 times .04???) and to go from 13 to 15 or 16 SEER (I have no idea how to calculate that potential cost savings) when I use the AC only May to September (sometimes April to October �it is very humid here in Maryland), I am not sure spending all that money is wise. My total gas and electric in the last 12 months was $3200.00. Gas is cheap. Electricity is not.

Contractor said that is what he would do if it were his house ($4300 option) plus simpler system � less costly parts/repairs and less to go wrong/break.

I think I agree with him.

Or am I thinking about this all wrong?

Thanks!

Comments (7)

  • mike_home
    9 years ago
    last modified: 9 years ago

    The difference in BTUs comes about because HVAC contractors are too lazy to do a proper load calculation. They use their rules of thumb which leads to different sizes.

    You started another thread so please post the size of your house. This will give an indication of sizing. If the current sizes maintained the desired temperatures, and the equipment did not short cycle, then that would indicate the current sizes are good.

    You are right that spending thousands of dollars more to gain a few percentage points on efficiency does not make sense. You can decide to spend more money that will make you more comfortable. I personally think a 2-stage variable speed furnace is money well spent. If you live in a high humidity area like I do, then a 2-stage AC condenser is also a good investment. Running on the low stage is a little more efficient, quieter, and more comfortable. It is like deciding on cloth versus leather seats in a car. It is all about additional comfort.

    The Carrier Comfort series is a basic furnace at the low end of the Carrier product line. The furnace is not as well built as the Performance and Infinity models. If you are planning to be in this house for another 10 years spend the extra money on a better furnace.

  • tigerdunes
    9 years ago
    last modified: 9 years ago

    A couple of things

    Don't make several different threads. Keep posts all in one thread, much easier for everyone to follow.

    Have dealers inspected your ductwork system? You have adequate returns on both floors of your home.

    I would go 3 ton on outside condenser whether single stage or two stage.

    Am Std is equal to and just as good as Carrier/Bryant.

    You will need a filter box cabinet for either system. I would not consider the Carrier Comfort quote, too low end.

    Ask AmStd dealer to upgrade you to 3 ton model Gold XI series single stage and Platinum XM 2 stage.

    Also you will need a two stage thermostat HW Prestige 2.0. Request from AS dealer.

    I don't trust your nat gas rate as being all inclusive. You shouldn't either. But not to worry because I will not recommend a DF system. Stay with high end nat gas furnace with high eff AC condenser.

    Post back with updated pricing and if you have further questions.

    IMO

  • Related Discussions

    Carrier Infinity vs American Standard Freedom 95

    Q

    Comments (3)
    A-S can't touch what all the Infinity control can do but for most people, it does more than they would ever use. The Freedom 95 with Honeywell Vision Pro IAQ would be all most need anyway. I personally am more of an A-S/Trane fan. As for the tax credits, I couldn't find any Carrier furnaces besides some 40,000 BTU models that met the 95% AFUE criteria in the downflow position. I guess some will report it anyway but if you are one who doesn't cheat on their taxes and have a downflow application, the Freedom 95 is the way to go.
    ...See More

    Trane vs Carrier

    Q

    Comments (6)
    Tiger - I will pull the information up and send to back later. DH says no one did a load calculation. Our upstairs Bedrooms are harder to cool - but hoping the new Hardi siding will help plus GC moved the upstairs vent and ran through basement and straight up instead of the original 4 corners from the original builder. DH usually balances the vents each spring/fall to maximize air flow for AC and heat. Thanks
    ...See More

    Carrier 96 or Carrier Comfort 92 or American Standard 97

    Q

    Comments (0)
    DELETED This post was edited by Carpediem12 on Thu, Aug 21, 14 at 0:35
    ...See More

    Carrier Infinity 21 a/c with 92% furnaces, 2 zone

    Q

    Comments (3)
    Zip Code 21234 is a Maryland zip. I am 21009 in Bel Air. FYI: A Carrier 21 SEER is not actually 21 SEER. Don't be fooled by the marketing bullsh%t. You should consider a heat pump w/gas furnace supplimentary heat (dual fuel or hybrid). You say it is not cost effective, but have you run the numbers? What is the delivered price of natural gas per therm? Post the model numbers of the heat pump condenser (or a/c condenser), matching indoor coil, and furnace, and we will provide the true SEER, EER, and HSPF from the American Refrigeration Institute. Good luck.
    ...See More
  • Carpediem12
    Original Author
    9 years ago
    last modified: 9 years ago

    Sorry for the confusion I caused with the new thread!

    The house is a 2 story colonial - 2,052 square feet plus a partially finished basement.
    How could I tell if the equipment was short cycling? I have been pretty comfortable with the exception of the second floor is sometimes hotter than the first floor in the summer- mostly addressed with the attic fan. I would not want to spend a lot of money to fix that. It has been a cool summer and not noticeable this year. That is why at least the one contractor that I asked did not think a two stage AC would be a good idea in this house. And why a 3 ton might be a better idea ��" although Manual J apparently says 2.5 ton (100% of cooling load ��" 26389 Btuh), if I understood what I read.

    Tigerdunes ��" what is a DF system (which you said you would not recommend)?

    Mike ��" I prefer leather seats in my cars! I was not sure I would actually be any more comfortable for the extra bucks since the rest of the house is from 1986.

    What should a contractor do to evaluate the ducts (if anything)? The ducts are not insulated as far as I can tell ��" just sheet metal. The house was built in 1986 with a heat pump system only. I converted to gas in 1996 ��" and I was thrilled to be able to do that.

    I calculated the cost of a therm by dividing therms used by total cost of gas on my bill ��" cost $1.28 per therm. I pay $13/month as a gas delivery charge whether I use any gas or not. I use about 560 therms/year (heating and cook top only).

    Using the same method, my total cost per kWh is $0.14 and I use about 19,000 kWh/year (everything else ��" hot water and clothes dryer, lights, etc).

    Contractor #1 did a Manual J and gave me the written report on software letter head (Wrightsoft Right J Mobile).

    Contractor #2 did not give me the Manual J but told me that he did it and it shows a total cooling load on the house using R19 insulation in my attic at 22,744 Btu's and a total cooling load at 21,750 using R30 insulation in the attic ��" which is not the same as the Manual J that I have in writing from Contractor #1??? According to Contractor #2, the Gold XI 2.5 ton A/C total cooling load at 95 degree outside temperature and 75 degree inside temperature is 24,400 Btu's. He said he could come back and take a closer look at the house if I would like. His original proposal has a 2.5 ton AC.

    Here is the updated pricing from Contractor #2:

    Proposal #1 - Supply and install an American Standard Gold ZM-80,000 Btu’s, 97% AFUE efficiency gas furnace and an American Standard Gold XI- 16 SEER 3 ton AC unit:

    AC AS 4A7A6036H1, single stage AC
    Furnace AS AUH2B080A9V3, 2 stage variable speed
    Coil AS 4TXCB036BC3 cooling coil.
    Thermostat AS digital programmable thermostat.

    Net cost to me $6,475.00

    Proposal #2 - Supply and install an American Standard Platinum ZV-80,000 Btu’s, 96.7% AFUE efficiency gas furnace and an American Standard Platinum ZM- 16.25 SEER 3 AC unit:

    AC AS 4A7A7036A1- 2 stage
    Furnace AS AUHM1B080ACV3 ��" 2 stage variable speed
    Coil AS model 4TNCB036AC3 cooling coil
    Thermostat Honeywell Prestige 2.0 digital programmable

    Net cost to me: $7,925.00

    Contractor #3 did not do a Manual J. I asked him for a price for the same Carrier equipment as Contractor #1 anyway. He said he was not able to do that because he did not inspect the work for an Infinity system. He would need to come back and look at the job to provide a price for the Infinity systems. That makes no sense to me because how could he give me a price on this system which was in his original proposal that contained the $4300 system? I had not included this option in my original post because it seemed like not a lot of bang for the extra bucks.

    AC Carrier Infinity 21 series two-stage 24ANB136A003 with a 3.0 ton cooling capacity
    Furnace Carrier Infinity 98 modulating gas furnace 59MN7080V17-14
    Coil Carrier Infinity all aluminum N series vertical evaporator coil with an insulated jacket CNVP3717ALA with a 3.5 ton cooling capacity
    Thermostat Carrier Infinity touch series WiFi SYSTXCCITNO1A
    Mechanical Air Cleaner: model #:EZXCABCC1020
    Power fan humidifier model #: HUMCCSFP1016

    Net cost to me after rebates and discounts: $8,465.00

    So one stage or 2 stage AC? 2.5 or 3 ton unit?

    Carrier or American Standard?

    Contractor 1 (5 year labor warranty through him), Contractor 2 (I think the 2 stage AC option might not be a good idea - 2 year labor ��" not sure if that is AS or him), or Contractor 3?

    What do you think of the Carrier 10 year labor warranty through Carrier?

    And thanks for your input! There were fewer choices 18 years ago. I am glad I am not sitting here with no heat doing this.

  • tigerdunes
    9 years ago
    last modified: 9 years ago

    I like AmStd just as good as Carrier.

    If you have confidence in the load calc for cooling, go 2 1/2 ton single stage, 3 ton for two stage AC condenser.

    On AmStd, quote #1 will require two stage thermostat like the HW Prestige 2.0 I recommended.

    For quote #2, it should be same furnace as quoted in quote #1, not the furnace dealer quoted. Ask for price to reviewed and updated. Cooling evap coils need to be reviewed by dealer for best application and best performance/ efficiency numbers in AC cooling.

    All systems whether Carrier or AmStd will require a filter media cabinet.

    DF stands for dual fuel, furnace with HP and I don't recommend.

    I will be unavailable for any comments for around 6-7 days minimum.

    Hope this helps.

    Good Luck
    IMO

  • mike_home
    9 years ago
    last modified: 9 years ago

    Short cycling is when the equipment go on and off for brief periods of time.

    "I calculated the cost of a therm by dividing therms used by total cost of gas on my bill ��" cost $1.28 per therm. I pay $13/month as a gas delivery charge whether I use any gas or not. I use about 560 therms/year (heating and cook top only)."

    You service charge comes out to about $.28 per therm. You are actually paying about $1 for each therm which is what I would expect. You should switch over to a gas hot water heater. The pay back would be fairly quick with a conventional tank.

    "Contractor #2 did not give me the Manual J but told me that he did it and it shows a total cooling load on the house using R19 insulation in my attic at 22,744 Btu's and a total cooling load at 21,750 using R30 insulation in the attic"

    That is an interesting calculation. Upgrading to R30 only saves 1000 BTUs of heat gain.

    If Contractor #2 calculated a 2 ton cooling load, why is he proposing a 3 ton AC condenser?

    "Contractor #3 did not do a Manual J. I asked him for a price for the same Carrier equipment as Contractor #1 anyway. He said he was not able to do that because he did not inspect the work for an Infinity system."

    I don't understand this statement. Infinity systems need properly sized duct work the same as all other Carrier equipment.

    I am always suspect of contractors who say a 2-stage AC might not work well in your house. I would like to understand the physics behind this.

    Carrier is not longer offering 10 year labor warranties. You have to get it from a third party. It is a good investment providing it is reasonably priced.

  • Carpediem12
    Original Author
    9 years ago
    last modified: 9 years ago

    Here is the updated quote from the American Standard contractor:

    Supply and install an American Standard Platinum ZV-80,000 Btu’s, 96.7% A.F.U.E efficiency gas furnace and an American Standard Platinum ZM- 16.25 S.E.E.R 3 ton air conditioning unit for your home.
    1- American Standard model AUHMB080ACV3 ��" 2 stage variable speed gas furnace.
    1- American Standard model 4A7A7036A1- 2 stage air conditioning unit.
    1- American Standard model 4NCB036AC3 cooling coil.
    1- Honeywell Prestige 2.0 digit programmable thermostat.
    1- Copper Line set.
    1- Composite pad.

    Net cost to me: $7925.

    Other than the 2 stage AC, is this apples to apples with the Carrier bid? Is the Carrier equipment a reasonable price for the equipment? Anything else I should consider?

    It is getting chilly so I better make a decision.

    Thanks.

  • tigerdunes
    9 years ago
    last modified: 9 years ago

    Before I take the time to give you any detailed analysis, you should know the Carrier and AmStd quotes while similar are not apples to apples particularly the furnaces.

    The Carrier is a two stage high eff model while the AmStd is a high eff modulating model. These modulating models allow for better comfort in small increments between a 40-100% range of BTU output. And if interested, AS dealer did not quote the proprietary thermostat control for full functionality of this furnace. If you are looking for a closer AS equivalent to the Carrier furnace, that would be the Gold ZM(identical to Trane's XV95 furnace).

    So you need to advise back the direction you are leaning toward.

    IMO

    This post was edited by tigerdunes on Fri, Sep 19, 14 at 16:01