Comments (45)No problem and I appreciate you being ok with me bumping into your exchange here- I am following this with alot of interest. Just quickly, on my issue, the installer came back out. At first he said this was normal as shared earlier and had to be told (from a non-expert) that this was not normal at all. It seems that he made some type of wiring adjustments (unknown since my wife cant follow any of this when she was watching and asking) and then adjusted settings within the setup of the Edge Thermidisstat. We are currently running oil heated-water baseboard as the backup and then the Performance series HP system (EER 12.5, SEER 15.5 and HSPF 9) cant find the AHRI# handy. Temps have been consistently at between 28 and 34 degrees here in Viginia for the last 5-7 days. We are having to manually switch from HP to the oil heat system for right now since I dont want this installer messing with anyting else to connect a relay that allows both to be working from the one thermostat. I will do that later (hence reason for following this discussion closely) I am tracking kW useage off the meter. Here's what I am seeing: Set the HP Edge at 68 degrees and it holds house temp steady wihtout having to use AUX at all. Set the oil heat-boiler at 66 setpoint(manual) It seems that only infrequently will the boiler kick on to augment the HP (running simul right now) Energy useage has been between 3.12 and 3.77 kW per hour across last 5 days (taken in 24 hr periods). VaPOwer is at about .06 cents per kW right now I think, so I'm looking at what 744 hours per month at avg 3.44 kW (.20 cents) per hour= $153.00/month. This is for a brick ranch, 1820 sq ft house...See Moredual fuel vs stand-alone heat pump
Comments (11)nash as far as nat gas,I think price will be more of a concern than supply and that the price difference between the two fuel sources will only widen. I am attaching a fuel comparison calculator for your use. I generally like straight high eff HPs with air handler and backup aux strips but with older homes not well insulated or tight envelope, then I think dual fuel is a better choice. Of course, you need a professionally performed heat/cool load calculation for correctly sizing new HVAC as well as ductwork to be thoroughly inspected for size, insulation qualities, leaks, etc. If you have any hot/cold spots in your home, now is the time to address these issues. here is a quick synopsis of Nashville climate from Trane's site. I personally think it underreports both cooling and heating but that's just my idea. anyway, it gives you an idea. Climate averages for: NASHVILLE, TN, 37203 Hot weather Cold weather Average days per year above 75: 153 Average high temperature: 88.7 Average days per year below 40: 31 Average low temperature: 36.8 I would not have a Lennox HP because of poor performance/eff numbers. Regardless of brand, you want a var speed blower whether air handler or furnace. BTW, what is the model of the upstairs HP? let me know if you have other questions. IMO Good Luck! Here is a link that might be useful: Fuel Comparison Calculator...See MoreDual Fuel Heat Pump w/ gas furnace or just heat pump?
Comments (17)I'm leaning towards just heat pump with heat strips. That should be fine for your area. If you plan on keeping it that warm in the house as you say in your OP, I would get the Bosch Inverter heat pump as it produces heat clear down to about 5-6 degrees ambient and very efficient at what it does. Then use the strip heat as you need it. I don't know that you'll find a contractor though for this for a new construction job as Bosch just recently came to the Houston market a few months ago. The distributor network for Bosch is in it's infancy... so there are pros and cons for choosing this brand. For what it does / how it does it --- it's a game changer for my market. (Katy, Texas area) As a comparison --- an average run of the mill single speed heat pump will probably struggle once temps drop into the 20's for any significant amount of time. They are efficient when compared to strip heat (utility bill cost wise) but there are higher limitations with those. I've gotten email notifications from my electric provider that they are estimating my next electric bill at less than $50 for November. This may wind up being my lowest electric bill ever for my power rate of 12 cents per KWH. With that said, I keep it quite chilly during the winter and my house is all electric (no gas at all). I shut it off at night and really just use it to take the chill out of the house in the morning. If it gets really cold here, I will probably just heat the main part of the house over night --- as I have it attached to a 4 zone duct system. (This is to explain the how and why my electric bill is so low -- design of the HVAC system is a big part of it.)...See Moreheat pumps in New England - All electric versus dual fuel
Comments (15)Re: mike_home I see a previous post by you has been deleted or taken down. Please don’t be ‘P.C’; there was nothing wrong or hostile about your post. We’re all ‘Long Distance’ friends here. Your question was fair and I’d like to answer it. I hope the reason for it no longer appearing is that you have answered it for yourself. So… “mike_home Fsq4cw, You said: the average cost to run a 5-ton Waterfurnace Series 7 in all but the most brutal conditions would probably be ~51¢/hr. Can you show how you calculate this operating cost?” Sure Mike, I’d be glad to help. OP says he lives in Boston Mass. So from, ‘Ground Source Heat Pumps’, ‘Appendix 1 – Ground Temperatures’ (Kavanaugh & Rafferty 1997), ground water temperature in Boston is 50˚F. Makes sense to me, I’m in Montreal Canada and our GWT is ~46˚F. I think it’s actually a little colder but these guys literally wrote the book on this subject. This GWT is easily found on the web for any North American city. Next, if you download the specs for the Waterfurnace Series 7 HP and ‘Drill Down’ through the specs (there’s a lot of them), on page 38 you will find the specs for the 5-ton HP (060). OP’s contractor says a 3-ton Mitsubishi air source HP would do most of the job, so why not for argument’s sake say a 5-ton would also do most of the job too. Water furnace Series 7 (060) Ground temperature in Boston is 50˚F. So let’s say after running for a long, long time the EWT (Entering Water Temperature) returning from the ground is really cold, say, 30˚F, 2-degrees below freezing (no problem, fluids contains glycol and should easily be able to go down into the lower 20’s˚ F). The performance data (page 38) on the ‘060’, a 5-ton HP on ‘Part Load’ 50%, these things like long run times and will scroll down once the set point is met. So EWT 30˚F, 6.3 GPM flow rate from the boreholes, 850-cfm from the blower, LAT (Leaving Air Temperature) from the HP to the main plenum would be 98.6˚F, Power kW (i.e. TOTAL HEAT PUMP POWER) 2.17kW. OP pays 23.6¢/kW x 2.17kW = ~51.21¢/hr. The only thing that matters is the heat loss of the envelope, outdoor temperature can go down to -60˚F, as long as the ground temperature is stable, nothing changes for the heat pump, COP remains constant. Minor changes in ground temperatures near the surface generally lag by at least 1-season, unlike the air temperature that can change hour to hour. Below about 12-feet there is much less change. Below 200-feet the ground temperature actually starts to rise, boreholes can be 450-feet deep for residential. Hope that helps, SR...See MoreRelated Professionals
Bridgeport Solar Energy Systems · Fort Lee Solar Energy Systems · Gardena Solar Energy Systems · Allen Home Automation & Home Media · Franklin Home Automation & Home Media · Half Moon Bay Home Automation & Home Media · Jollyville Home Automation & Home Media · Pittsburgh Home Automation & Home Media · Washington Home Automation & Home Media · West Palm Beach Home Automation & Home Media · Weston Home Automation & Home Media · Worcester Electricians · Ashland Electricians · Atlanta Fireplaces · Monroe Fireplaces- 7 years ago
- 7 years ago
- 7 years ago
- 7 years ago
- 7 years ago
- 7 years ago
- 7 years ago
Related Stories

BARN HOMESHouzz Tour: An Energy-Efficient Barn Graces the Nebraska Landscape
Passive-house technologies and a rain-harvesting and greywater system conserve natural resources in this weekend country home
Full Story
LIVING ROOMS8 Reasons to Nix Your Fireplace (Yes, for Real)
Dare you consider trading that 'coveted' design feature for something you'll actually use? This logic can help
Full Story
GREEN BUILDINGHouzz Tour: See a Maine House With a $240 Annual Energy Bill
Airtight and powered by the sun, this energy-efficient home in a cold-winter climate is an architectural feat
Full Story
FIREPLACESUpdated Woodstoves Keep Home Fires Burning
Better technology means more efficiency than ever for modern woodstoves
Full Story
GREEN BUILDINGHouzz Tour: Pickle Factory Now an Energy-Wise Live-Work Space
A charming but poorly insulated 1880s Philadelphia commercial building becomes a spacious energy-efficient home and studio
Full Story
GREAT HOME PROJECTSHow to Switch to a Tankless Water Heater
New project for a new year: Swap your conventional heater for an energy-saving model — and don’t be fooled by misinformation
Full Story
LIVING ROOMSHow to Convert Your Wood-Burning Fireplace
Learn about inserts and other options for switching your fireplace from wood to gas or electric
Full Story
SAVING WATER11 Ways to Save Water at Home
Whether you live in a drought-stricken area or just want to help preserve a precious resource, here are things you can do to use less water
Full Story
GREEN BUILDINGZero Net Energy: A Hardworking-House Term to Know
Homes that consume only as much energy as they produce by renewable means are a goal for builders. Learn what ZNE means for you
Full Story
LIFEThe Top 5 Ways to Save Water at Home
Get on the fast track to preserving a valuable resource and saving money too with these smart, effective strategies
Full Story
mike_home