Trane 5 Ton Heat Pump Estimate Received----Opinions, Please!
User
8 years ago
last modified: 8 years ago
Featured Answer
Sort by:Oldest
Comments (22)
tigerdunes
8 years agoUser
8 years agolast modified: 8 years agoRelated Discussions
Lennox vs Trane vs Rheem Heat Pump systems
Comments (4)After reading more carefully, it seems your sizing estimates are all over the place, from 2.5 ton (Lennox), to 3 ton (Trane), to 4 ton (Rheem). A properly done load calculation is necessary to get the equipment size right, especially since you've made changes to your home's structure. Now would also be a good time to have your ductwork balanced so that each room gets the required airflow per the load calculation. Before investing money in a new system, it is very important to ensure your new system is operating at its rated capacity and efficiency....See MoreReplacing a 20 year old Trane Unit 2.5 ton
Comments (65)Heres a Link: http://www.greenbuildingadvisor.com/blogs/dept/musings/saving-energy-manual-j-and-manual-d Even when they do the calculations, the results are usually wrong In his posted comment, Bailes raised an interesting point: the problem of “garbage in, garbage out” (GIGO) Manual J calculations. Several energy experts have commented on the GIGO problem, including John Proctor, Hank Rutkowski, and Allison Bailes. Hank Rutkowski, the mechanical engineer who wrote the original Manual J document, was recently interviewed for a profile posted on the Green Building Talk Web site. The piece notes, “Rutkowski estimates that only 10% of heating and cooling equipment sizing decisions are based on some type of Manual J calculation and that less than 1% of the jobs are based on an aggressive implementation of the recommended design procedures.” Rutkowski explains the GIGO problem this way: “Manual J is a good tool if you use it aggressively. Follow the rules and it will give you a reasonable margin of safety. But the average contractor says, ‘Better safe than sorry,’ so he fudges here and there. He adds 5 to 10 degrees to the summer and winter design temperatures, calls the building ‘average’ instead of ‘tight’ and doesn't take credit for shading by interior blinds and drapes. Then when he finally comes up with a load number for sizing, he throws in an extra half-ton of AC just for the heck of it.” For a high-performance home, sizing by Manual J may still result in oversizing Several years ago, I had a conversation with building scientist Joe Lstiburek about air conditioners installed in Building America homes in Las Vegas. “HVAC designers are committed to the institutional oversizing of air conditioning equipment,” Lstiburek told me. “The average system is sized at 150% to 200% of the requirements of Manual J. They oversize because they don’t know what they will get for a building envelope, and to compensate for duct leakage and inappropriate refrigerant charge. If you size according to Manual J, there is already a fudge factor built in. But most designers then add another fudge factor.” According to Lstiburek, their experience proved the high-performance Building America homes in Las Vegas could have had HVAC systems sized at about 60% of Manual J. To be conservative, his team recommended installing systems sized at 80% of Manual J. Does oversizing matter? There are strong arguments against routine oversizing of HVAC equipment. The best argument is simple: oversized equipment usually costs more than right-sized equipment. Oversized equipment suffers from short cycling. For example, an oversized furnace brings a home up to temperature quickly, and then shuts off. A few minutes later, it comes on again, only to shut off quickly. Many homeowners find the see-saw sound of a short-cycling furnace to be annoying. When air conditioners short cycle, the units don't run long enough to achieve much dehumidification ��" at least in theory. (During the first few minutes of operation, an air conditioner cools a house. But not enough moisture has collected on the cold coil or on the pan below for any water to have actually gone down the drain. When the air conditioner turns off, all of the moisture in the pan and on the coil just re-evaporates.) The conventional wisdom may be wrong, however Increasing evidence shows that energy experts have exaggerated the negative effects of equipment oversizing, however. Studies have confirmed that oversized furnaces don't use any more energy than right-sized furnaces. Moreover, newer modulating or two-speed furnaces operate efficiently under part-load conditions, solving any possible problems from furnace oversizing. Although there are ample reasons to believe that oversized air conditioners are less effective than right-sized equipment at dehumidification, at least one field study was unable to measure any performance improvements or energy savings after replacing an existing oversized air conditioner with a new right-sized unit. The bottom line The main reason to choose right-sized equipment is to avoid paying too much money for equipment you don't need. A Manual J calculation will ensure you don't spend more than necessary for your furnace, boiler, or air conditioner. Moreover, a Manual J calculation will provide room-by-room heat loss and heat-gain information that is essential to good duct design. Without good duct design, you're running the risk of comfort complaints....See Moretwo trane xl15i heat pumps bids
Comments (2)I wouldn't recommend the TUX1D furnace over the TUH2D (variable speed), especially for more money. Ask dealer 2 why he's quoting a 5 ton versus the 4 ton in estimate 1. A load calculation needs to be done. Overall dealer 2 is quoting larger equipment. I thought the furnace had a 10 year warranty if registered online with Trane within 60 days - something to ask about. The prices do not sound all that unreasonable since it includes all ductwork and a dual fuel, high end heat pump system. You should be getting a better thermostat, such as the Honeywell IAQ or TCONT802. I would expect around a $10k price tag since it's a complete installation with new ductwork. Looks like your area's prices, or these dealers' prices, are running higher. I'd get another estimate....See More2.5 ton vs 3 ton pkg'd heat pump
Comments (2)Claire How did your old 2 1/2 ton pkg unit perform? You are certain it is a 2 1/2 ton? More is not better. Can cause short cycling, poor dehumidification in AC mode, and can shorten equipment life. not to mention higher operating cost. What size heat strip is quoted by Trane dealer? Without more info to support a 3 ton choice, I would stick with the Trane. IMO...See Moretigerdunes
8 years agoweedmeister
8 years agolast modified: 8 years agoUser
8 years agotigerdunes
8 years agolast modified: 8 years agoUser
8 years agolast modified: 8 years agomike_home
8 years agotigerdunes
8 years agolast modified: 8 years agomike_home
8 years agoUser
8 years agolast modified: 8 years agoUser
8 years agomike_home
8 years agoUser
8 years agomike_home
8 years agoUser
8 years agolast modified: 8 years agoudarrell
8 years agomike_home
8 years agoUser
8 years agoweedmeister
8 years agomike_home
8 years ago
Related Stories
GREAT HOME PROJECTSHow to Add a Radiant Heat System
Enjoy comfy, consistent temperatures and maybe even energy savings with hydronic heating and cooling
Full StoryGREEN BUILDINGInsulation Basics: Heat, R-Value and the Building Envelope
Learn how heat moves through a home and the materials that can stop it, to make sure your insulation is as effective as you think
Full StoryFLOORSIs Radiant Heating or Cooling Right for You?
Questions to ask before you go for one of these temperature systems in your floors or walls (yes, walls)
Full StoryMOST POPULAR5 Remodels That Make Good Resale Value Sense — and 5 That Don’t
Find out which projects offer the best return on your investment dollars
Full StoryREMODELING GUIDES5 Ways to Protect Yourself When Buying a Fixer-Upper
Hidden hazards can derail your dream of scoring a great deal. Before you plunk down any cash, sit down with this
Full StoryCONTRACTOR TIPSLearn the Lingo of Construction Project Costs
Estimates, bids, ballparks. Know the options and how they’re calculated to get the most accurate project price possible
Full StoryKITCHEN DESIGN5 Favorite Granites for Gorgeous Kitchen Countertops
See granite types from white to black in action, and learn which cabinet finishes and fixture materials pair best with each
Full StoryWORKING WITH AN ARCHITECTWho Needs 3D Design? 5 Reasons You Do
Whether you're remodeling or building new, 3D renderings can help you save money and get exactly what you want on your home project
Full StoryDOORS5 Questions to Ask Before Installing a Barn Door
Find out whether that barn door you love is the right solution for your space
Full StoryKITCHEN DESIGNKitchen Recipes: Secret Ingredients of 5 One-of-a-Kind Cooking Spaces
Learn what went into these cooks’ kitchens — and what comes out of them
Full Story
UserOriginal Author