usual for a residential oven/range to need over 50 amps?

I was called out to a house that was just sold to fix a range/oven that trips the breaker when all burners are on. Naturally the circuit was wired with 8/2 with ground and a 40 amp breaker despite being built only 25 years ago. When I looked at the nameplate of the oven it said a little over 13 kw. The cord it was equiped with was #6 with a 50 amp cord cap. I put in new 6/3 with ground and rewired the oven for 4-wire. Put the oven on clean, all burners to full and my ct measured 54 amps. Is this normal? Just a kind of cheap looking amana oven. Do they assume no-one will use everything at once making a 50 amp circuit adequate?