245 Haldey Ave Oakwood Ohio
This will give you an idea of what the house is really like, before you go see it, or sign a contract.
Property Address:
245 Hadley Avenue
Dayton OH 45419
Inspection Date: 4/24/2010
Table of Contents
Cover Page
 Table of Contents
 Intro Page
 1 ROOFING
 2 EXTERIOR ELEMENTS
 3 SITE ELEMENTS
 4 GARAGE
 5 ATTIC
 6(A) BATHROOM, 2nd floor
 6(B) BATHROOM, basement
 7 KITCHEN
 8 INTERIOR ELEMENTS
 9 FOUNDATION / SUBSTRUCTURE
 10 FOUNDATION AREA WATER PENETRATION
 11 ELECTRIC SYSTEM
 12 COOLING SYSTEM
 13 HEATING SYSTEM
 14 PLUMBING SYSTEM
 15 WATER HEATER
 Attachments
 Invoice
INSPECTION DETAILS
DESCRIPTION:
Single Family House TYPE OF INSPECTION:
Standard Home Inspection AGE:
80 Years
Reported Year : 1930
STATUS:
Vacant WEATHER:
Overcast; Rain TEMPERATURE:
55-60 F.
PEOPLE PRESENT:
No One AUTHORIZED DISTRIBUTION:
Client(s), Client's Agent DIRECTION STRUCTURE FACES (APPROX.):
South
ANCILLARY SERVICES:
Radon Testing RADON TESTING:
See ATTACHEMENTS section
Top Table of Contents Bottom
1. ROOFING
ROOF STYLE:
Moderate Slope
"Dutch Colonial" Style MATERIAL:
3-tab (asphalt/fiberglass) shingle (standard weight) ESTIMATED AGE:
Over 15 years
DESIGN LIFE:
16 to 20 years LOCATION:
House INSPECTION METHOD:
Ladder at Eaves
Walked on Lower Area(s)
EXTERIOR OF CHIMNEY/VENT:
Brick
Water Heater
Location : center SPECIAL LIMITATIONS:
Height/Design
S F P NA NI
1.0 ROOFING
Due to cracked shingles, nail protrusions; Obtain estimate on roof replacement/roofer opinion.
3-4 areas where shingles have been replaced.
1.1 EXPOSED FLASHING
Appear to be recent repairs.
1.2 EXTERIOR OF CHIMNEY/VENT
Mortar gaps, loose bricks (note that this is only in use for the water heater and there appears to be a metal flue).
1.3 VENTILATION COVERS
1.4 PLUMBING STACKS
1.5 RAIN GUTTERS
Leaves/debris.
1.6 DOWNSPOUTS / ROOF DRAINS
1.7 DOWNSPOUTS
Splashblock/extension not in place at NE corner.
1.8 FASCIA / SOFFITS
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
1.0 ROOFING Picture 1
1.0 ROOFING Picture 2
1.0 ROOFING Picture 3
1.0 ROOFING Picture 4
1.0 ROOFING Picture 5
1.1 EXPOSED FLASHING Picture 1
1.2 EXTERIOR OF CHIMNEY/VENT Picture 1
Top Table of Contents Bottom
2. EXTERIOR ELEMENTS
SIDING:
Vinyl PORCH:
Covered
Concrete Slab
Concrete Foundation
Location : front (south) DECK:
Wood Frame
Partially Covered
Location : rear
DECK #2:
Wood/Platform On Grade
Location : rear SPECIAL LIMITATIONS:
Under Deck: Inaccessible
S F P NA NI
2.0 SIDING
Minor cosmetic/mAINTENANCE.
2.1 TRIM
2.2 WINDOWS
Exception: some torn screens.
2.3 ENTRY DOOR(S)
2.4 STEPS
Uneven rise.
2.5 PORCH
2.6 DECK
2.7 DECK #2
2.8 RAILINGS
2.9 ELECTRIC / GFCI
(1) Front: cracked (2-prong) receptacle.
(2) Below deck and at NW corner of deck: wiring not in conduit.
(3) NW corner of deck: cover missing at receptacle.
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
2.9 (2) ELECTRIC / GFCI Picture 1
3. SITE ELEMENTS
WALKWAY:
Wood/Platform CITY SIDEWALK:
Concrete DRIVEWAY:
Predominate: asphalt
Concrete (partial)
SPECIAL LIMITATIONS:
Common Elements
Under Deck: Inaccessible
S F P NA NI
3.0 WALKWAYS
3.1 WALKWAY - CITY SIDEWALK
3.2 STEPS
3.3 DRIVEWAY
(1) Settlement; settlement cracks at concrete area (near garage).
(2) Patched asphalt near city sidewalk.
3.4 WINDOW WELLS
High mulch levels (some with depressions at windows).
3.5 GROUND SLOPE AT FOUNDATION
Generally level; some depressions.
3.6 SITE GRADING
Generally level.
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
3.4 WINDOW WELLS Picture 1
4. GARAGE
DESCRIPTION:
Detached, Wood Frame, 2-car
Wood Rafters
OSB Sheathing
Concrete Foundation
Concrete (Floating) Slab ROOF DESCRIPTION:
Moderate Slope ROOF MATERIAL:
3-tab asphalt/fiberglass shingle (sandard weight)
ROOF ESTIMATED AGE:
1 to 5 years ROOF DESIGN LIFE:
16 to 20 years ROOF INSPECTION METHOD:
Walked On
SIDING:
Vinyl INSULATION:
Suspect at Walls ATTIC INSPECTION METHOD:
Visible (open framing)
SPECIAL LIMITATIONS:
Panels/paneling
Insulation
S F P NA NI
4.0 ROOFING
4.1 GUTTERS/DOWNSPOUTS
Exception: splashblock(s)/extension(s) not present.
4.2 TRIM
4.3 SERVICE DOOR
4.4 WINDOW(S)
Sided-over.
4.5 VEHICLE DOOR(S)
4.6 DOOR OPERATOR(S)
Disconnected; power cord cut. Advanced age unit.
4.7 EXPOSED FRAMING
Paneling present.
4.8 EXPOSED FRAMING - MISC.
Rafters and rafter ties.
4.9 WALLS
Delamination; loose panels (cosmetic/maintenance).
4.10 FOUNDATION
Settlement/cracks (does not appear to have adverse conditions). Limitation at rear (stored items/debris).
4.11 FLOOR SLAB
Typical tight settlement cracks.
4.12 ELECTRIC / GFCI
4.13 LIGHTING/FIXTURES
Exterior: not possible to check due to photo-cell control.
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
4.7 EXPOSED FRAMING Picture 1
4.7 EXPOSED FRAMING Picture 2
4.10 FOUNDATION Picture 1
5. ATTIC
DESCRIPTION:
Exposed Framing
Pull-Down Stairs INSPECTION METHOD:
Entered FRAMING:
Wood Frame
Rafters
SHEATHING:
Wood Composite (OSB) VENTILATION PROVISIONS:
Location: Gable Ends
Location: Rooftop INSULATION - PREDOMINATE:
Blankett/Batt
Fiberglass
4 to 6 Average Inches
SPECIAL LIMITATIONS:
Floored areas
Insulation
S F P NA NI
5.0 ROOF FRAMING
5.1 ROOF DECK / SHEATHING
OSB over spaced-boards.
5.2 VENTILATION PROVISIONS
5.3 ATTIC VENTILATOR(S)
Attic air temperature too low to activate thermostat.
5.4 INSULATION
Near current day's standards.
5.5 PULL-DOWN STAIR
Bent/misaligned metal braces (impedes closing).
5.6 WIRING
(1) Exposed splice at gable-end ventilator.
(2) Exposed splice at whole-house fan.
5.7 WHOLE HOUSE FAN
Motor turns, but belt slips (not enough air movement to open louvers).
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
5.6 (1) WIRING Picture 1
5.6 (2) WIRING Picture 2
6(A). BATHROOM, 2nd floor
DESCRIPTION:
Full Bath VENTILATOR(S):
Combo Fan/Light
S F P NA NI
6.0.A SINK (left side)
6.1.A SINK (right side)
Drain mechanism needs adjustment to fully close.
6.2.A TOILET
6.3.A TUB/SHOWER COMBO
6.4.A SURROUNDS / ENCLOSURES
Molded unit.
6.5.A WALLS / CEILING / FLOORING
6.6.A VENTILATION
Vents to attic (dated method).
6.7.A ELECTRIC / GFCI
6.8.A DRAINAGE
Very slow at bathtub.
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
6(B). BATHROOM, basement
DESCRIPTION:
3/4 Bath VENTILATOR(S):
Exhaust Fan
S F P NA NI
6.0.B SINK(S)
6.1.B TOILET
6.2.B STALL SHOWER
Hot/cold reversed.
6.3.B SURROUNDS / ENCLOSURES
Molded unit. Exception: glass door needs adjustment to latch closed.
6.4.B CEILING
6.5.B WALLS
(1) Gaps/openings.
(2) Stains behind toilet, near door.
6.6.B FLOOR(ING)
6.7.B VENTILATION
6.8.B ELECTRIC / GFCI
3-prong not grounded/not GFCI.
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
6.5.B (1) WALLS Picture 1
6.5.B (2) WALLS Picture 2
6.5.B (2) WALLS Picture 3
NOTE: Anticipate the possibility of leakage or other concerns developing with normal Top Table of Contents Bottom
7. KITCHEN
FREESTANDING RANGE/OVEN:
Electric
Estimated Age: 1 to 5 years DISHWASHER:
Estimated Age: 6 to 10 years DISPOSAL:
Estimated Age: 6 to 10 years
VENTILATOR:
Incorporated into microwave oven REFRIGERATOR:
Not Present MICROWAVE:
Estimated Age: 1-5 years
S F P NA NI
7.0 PLUMBING / SINK
7.1 WALLS / CEILING
7.2 FLOOR(ING)
7.3 ELECTRIC / GFCI
East wall.
7.4 ELECTRIC / GFCI
No receptacles at west countertop areas.
7.5 COOKING UNIT
Anti-tip bracket not installed. Recommend installing an anti-tip bracket at the range unit as required by the manufacturers installation instructions to limit the risk of tip over when the oven door is open. Warning tag is present on the inside of the oven door.
7.6 DISHWASHER
Age.
7.7 DISPOSAL
Age, corrosion at housing.
7.8 DISPOSAL WIRING
Exposed wiring at underside of disposal - recommend repair by electrician.
7.9 VENTILATOR
Recirculating.
7.10 CABINETRY
7.11 COUNTERTOP
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
7.8 DISPOSAL WIRING Picture 1
Report ID# Y0424-1 / Rieser
8. INTERIOR ELEMENTS
CEILINGS:
Wood Frame WALLS:
Wood Frame FLOORS:
Wood Frame
WINDOWS - PREDOMINATE:
Double Hung
Sliders
Insulated glass
w/Screens WINDOWS:
Casement
Single Glaze
w/Storm Windows
Location : stairway DETECTOR(S):
Not Inspected
Battery
DETECTOR LOCATION(S):
1st Floor
2nd Floor
Basement
Each Bedroom FIREPLACE:
None Observed
S F P NA NI
8.0 CEILINGS
8.1 WALLS
8.2 FLOORS (FRAMED)
8.3 STAIRS
8.4 RAILINGS
8.5 WINDOWS
Exception below.
8.6 WINDOWS - MISC.
Rear window at living-room: damaged catches for the tilt-in mechanism (does not stay in track).
8.7 ROOM DOORS
Some need adjustment/sanding to open/close smoothly.
8.8 AUXILIARY SYSTEMS/COMPONENTS
Auxiliary items such as security/safety systems (or the need for same), home entertainment or communication systems, structured wiring systems, doorbells, telephone lines, central vacuums, and similar components are not included in a standard home inspection.
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
9. FOUNDATION / SUBSTRUCTURE
CONSTRUCTION TYPE:
Basement BASEMENT AREA(S):
Full House
Finished Area(s) CRAWLSPACE AREA(S):
None Observed
FOUNDATION WALLS/PIERS:
Concrete FLOOR STRUCTURE:
Wood Frame
Joist
Wood Post
Metal Screw Jack
Wood Beam(s) INSULATION:
Not Determined at Finished Areas
SPECIAL LIMITATIONS:
Finish Materials
Suspended/Drop Ceiling
Insulation
Carpeting/Floor Coverings
Coatings
S F P NA NI
9.0 FOUNDATION WALLS
Finished walls.
9.1 FRAMING
Finished/suspended ceilings.
9.2 FRAMING - MISC.
Termite damage at visible area at framing at stairway. Recommend further evaluation and check of hidden areas.
9.3 PIERS / COLUMNS
Where visible.
9.4 MAIN BEAM(S)
Finished areas.
9.5 BASEMENT FLOOR (SLAB)
Carpeted.
9.6 STAIRS
9.7 RAILING(S)
Rail/guard not present at one side (over 3 steps - open to basement).
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
9.0 FOUNDATION WALLS Picture 1
9.0 FOUNDATION WALLS Picture 2
9.0 FOUNDATION WALLS Picture 3
9.0 FOUNDATION WALLS Picture 4
9.2 FRAMING - MISC. Picture 1
9.7 RAILING(S) Picture 1
Top Table of Contents Bottom
10. FOUNDATION AREA WATER PENETRATION
AREAS AT GRADE/SUBGRADE:
Basement SUMP PUMP:
Not Observed SPECIAL LIMITATIONS:
Finish Materials
Suspended/Drop Ceiling
Insulation
Coated/Painted Walls or Surfaces
Carpeting/Floor Coverings
S F P NA NI
10.0 EXTERIOR FEATURES / WATER INTRUSION FACTORS
Level grading adjacent to foundation.
10.1 INTERIOR CONDITIONS / SIGNS OF WATER PENETRATION CONDITIONS
(1) Mold/mildew stains at corners/rear of basement.
(2) Water marks/stains at base of framing where visible at utility area.
(3) Flaking coatings/surfaces where visible.
10.2 INDICATIONS OF PRIOR REMEDIAL WORK
No visible evidence of waterproofing and/or mold/mildew remediation - recommend obtaining information from seller.
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
10.1 (1) INTERIOR CONDITIONS / SIGNS OF WATER PENETRATION CONDITIONS Picture 1
10.1 (1) INTERIOR CONDITIONS / SIGNS OF WATER PENETRATION CONDITIONS Picture 2
10.1 (1) INTERIOR CONDITIONS / SIGNS OF WATER PENETRATION CONDITIONS Picture 3
10.1 (1) INTERIOR CONDITIONS / SIGNS OF WATER PENETRATION CONDITIONS Picture 4
10.1 (1) INTERIOR CONDITIONS / SIGNS OF WATER PENETRATION CONDITIONS Picture 5
10.1 (2) INTERIOR CONDITIONS / SIGNS OF WATER PENETRATION CONDITIONS Picture 6
10.1 (2) INTERIOR CONDITIONS / SIGNS OF WATER PENETRATION CONDITIONS Picture 7
Top Table of Contents Bottom
11. ELECTRIC SYSTEM
ELECTRIC SERVICE:
Service Line: Overhead
Est. Service Capacity: 120/240 Volts; 100 Amps
Type Service Feeder: Aluminum
Est. Feeder Capacity: 100 Amps DISTRIBUTION PANEL:
Type: Circuit Breaker Panel
Est. Capacity: 125 Amps
Main Disconnect: 100 Amps
Location: Basement PANEL CIRCUITS:
120 Volt Circuits: Copper Wire
240 Volt Circuits: Copper & Aluminum
PANEL BRAND:
Square D CIRCUIT-INTERRUPTERS:
GFCI: At Receptacle Outlet(s)
AFCI: None Observed
S F P NA NI
11.0 SERVICE / ENTRANCE LINE
11.1 SERVICE GROUNDING PROVISIONS
11.2 METER/BOX
Crimping tag (seal) not present; contact utility company (anticipate 6-8 week wait to install crimping tag).
11.3 MAIN DISCONNECT(S)
11.4 DISTRIBUTION PANEL
Exception below.
11.5 CIRCUIT / CIRCUIT BREAKER(S)
Circuit #7: 14 gauge conductor on 20 amp breaker (repair needed for safety) - oversized beakers (or undersized wires) are a hazard and must be corrected.
11.6 DEVICES
Most are 2- prong receptacles (dated method).
11.7 DEVICES - MISC.
(1) Receptacles not "live" at NE bedroom (behind door) and at west wall of dining room (shelf area). Recommend repair/further evaluation.
(2) Indeterminate if failed bulb or fixture/wiring defect at 2nd floor hallway light fixture and at two basement light fixtures. Recommend repair/further evaluation.
(3) Exposed wiring at light fixture/rack at SW corner of basement.
11.8 WIRING / CONDUCTORS
Most is 2-wire without grounding conductor (dated method). Some knob and tube in use.
11.9 ELECTRIC DISTRIBUTION
Limited number of circuits/receptacles by today's standards.
11.10 GFCI TEST
11.11 240 VOLT RECEPTACLES
3 prong (dated design).
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
11.2 METER/BOX Picture 1
11.7 (3) DEVICES - MISC. Picture 1
11.8 WIRING / CONDUCTORS Picture 1
Top Table of Contents Bottom
12. COOLING SYSTEM
SYSTEM TYPE:
Electric Central Air Conditioning
Capacity : 2-ton BRAND:
Inter-City SYSTEM LOCATION:
Split System (outdoor and indoor components)
Basement
Exterior at Rear
ESTIMATED AGE:
18 years
Year : 03/1992 DESIGN LIFE:
6 to 10 years GENERAL DISTRIBUTION:
Ducted/Registers
Individual Room Supply
S F P NA NI
12.0 COOLING SYSTEM
Only 8-10 degrees (F.) drop between return and supply. Recommend further evaluation/repair.
Advanced age (1992). Anticipate repair/recharges/replacement. Review comments in SUPPLEMENTAL INFORMATION regarding replacement air conditioner / heat pump efficiency requirements.
12.1 OUTDOOR UNIT(S)
See above.
Age/corrosion.
12.2 INDOOR BLOWER / FAN
12.3 CONDENSATE PROVISIONS
12.4 THERMOSTAT
12.5 DISTRIBUTION
No second floor return observed (anticipate stratification). Consider leaving fan in ON position (especially during cooling season) and balancing system in between heating and cooling seasons.
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
12.1 OUTDOOR UNIT(S) Picture 1
13. HEATING SYSTEM
SYSTEM TYPE:
Hot Air
Fuel: Natural Gas
BTU Input : 69,000 (output: 64,000) BRAND:
Goodman SYSTEM LOCATION:
Basement
ESTIMATED AGE:
5 years
Year : 2005 DESIGN LIFE:
16-20 years GENERAL DISTRIBUTION:
Ducted/Registers
Individual Room Supply
Filter Location : to right of furnace
SPECIAL LIMITATIONS:
Limited view of heat exchanger due to design SYSTEM MAKE - SECONDARY:
Indeterminate ESTIMATED AGE - SECONDARY:
16-20 years
DESIGN LIFE - SECONDARY:
18-25 years
S F P NA NI
13.0 HEATING UNIT
Operating as expected.
13.1 GAS / FUEL LINES AT UNIT
13.2 VENT CONNECTOR
Horizontal PVC to exterior.
13.3 BLOWER
13.4 THERMOSTAT(S)
13.5 DISTRIBUTION SYSTEM
13.6 EXPOSED DUCTWORK
Gap/opening visible at right side of supply plenum.
13.7 EXPOSED DUCTWORK - MISC.
Suspect asbestos-containing panels at return ducts and in ductape - recommend further evaluation.
13.8 ELECTRONIC AIR CLEANER
Not "popping/snapping" as expected (recommend service/maintenance).
13.9 HEATING #2
(1) Only one of the three radiant ceiling panels heats up.
(2) Thermostat: loose temperature setting cover.
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
13.6 EXPOSED DUCTWORK Picture 1
13.7 EXPOSED DUCTWORK - MISC. Picture 1
13.7 EXPOSED DUCTWORK - MISC. Picture 2
13.7 EXPOSED DUCTWORK - MISC. Picture 3
13.9 (1) HEATING #2 Picture 1
14. PLUMBING SYSTEM
WATER PIPING:
Copper WATER SHUT-OFF LOCATION:
At Meter
Basement GAS SHUT-OFF LOCATION:
At Meter(s)
At Exterior
DRAIN/WASTE LINES:
Predominate: Cast Iron
Galvanized
Plastic WATER TREATMENT SYSTEM(S):
Filter
Water Softener (Not in Use) SPECIAL LIMITATIONS:
Finished Area(s)
S F P NA NI
14.0 WATER PIPING
14.1 WATER PIPING - MISC.
Piping through east wall of basement: discharges to open-ended pipe at exterior (purpose indeterminate - recommend obtaining information from seller).
14.2 WATER FLOW AT FIXTURES
14.3 DRAIN / WASTE PIPING
Age/corrosion. Dated venting methods.
14.4 FIXTURE DRAINAGE
Vacant home. It is often not possible to properly evaluate certain elements if a house has been vacant for any length of time. For example, a drain leak in a wall or blockage in an underground waste line may not become apparent until hours (or days) after the inspection. Therefore, anticipate the possibility of such latent defects with subsequent use of the house and/or systems. Note: water was run at a bathtub and/or laundry drain for 30-45 minutes.
Exception noted at 2nd floor bathroom.
14.5 EXTERIOR FAUCET(S)
East: not freeze-bib (dated method).
14.6 EXTERIOR FAUCET(S)
West: handle does not turn with reasonable force. Not freeze-bib (dated method).
14.7 LAUNDRY HOOKUP
Hot/cold reversed.
14.8 GAS PIPING
14.9 WATER SOFTENER
Older, mechanical design. Not in use (not plugged in). The function and effectiveness water filtration or treatment equipment is not evaluated. Recommend obtaining information from seller.
14.10 FILTER/SYSTEM(S)
The system appears to be in use with no visible leakage. The function and effectiveness water filtration or treatment equipment is not evaluated. Recommend obtaining information from owner.
14.11 FLOOR DRAIN(S)
Clogged (backed-up after running water for 10-15 minutes).
S F P NA NI
S=Satisfactory, F=Fair, P=Poor, NA=Not Applicable, NI=Not Inspected
Review REPORT TERMINOLOGY on Introduction Page. Consult with your Inspector for clarification on ratings or findings if there are any questions.
14.1 WATER PIPING - MISC. Picture 1
14.9 WATER SOFTENER Picture 1
15. WATER HEATER
WATER HEATER TYPE:
Direct-heated Tank
Fuel: Natural Gas WATER HEATER LOCATION:
Basement ESTIMATED CAPACITY:
40 Gallons
BRAND:
Bradford-White ESTIMATED AGE:
4 years
Year : 2006 DESIGN LIFE:
10-12 years
S F P NA NI
15.0 WATER HEATER
15.1 VENT CONNECTOR
15.2 GAS / FUEL LINES AT UNIT
15.3 SAFETY VALVE PROVISIONS