Honeywell VisionPro IAQ, a pre-install question

15 years ago

I'm about to self-install a Honeywell VisionPro IAQ and had a question about wiring the blower-speed control for dehum function.

In the Installation Manual for my furnace (Bryant 333BAV two stage gas w/ older Goodman 3.5ton single stage AC) it says the following:

4. As an alternative to selecting 315 CFM per ton for cooling

airflow, additional dehumidification on demand can be

achieved with use of a field-supplied humidistat. Remove

the factory-installed GREEN wire marked DEHUM from

the 1/4-in. quick-connect at the G terminal on furnace

control. Connect a humidistat that opens-on-humidity-rise

between the green wire marked DEHUM and the G terminal

on the furnace control. When humidistat contacts open,

airflow will be reduced to 80 percent of selected airflow,

but not less than 280 CFM per ton.

I'm interpreting this to mean I need to run a wire from Dehum2 on the IAQ board to the G terminal on the furnace control board in addition to the wire from G on the IAQ to G on the furnace control. So terminal G on the furnace control board would actually have two wires from the IAQ attached to it?

I've included a link to the Install Manual for my furnace if it helps you help me.

Thanks

JG

Here is a link that might be useful: 333BAV Installation Manual