SHOP PRODUCTS
Houzz Logo Print
cofloater

humidifier cuts off furnace burner prematurely

cofloater
11 years ago

After I installed the copper water supply lines and PVC drain lines, I had a contractor install two Honeywell TrueEASE HE200 humidifiers on my two older SnyderGeneral furnaces. They are simple humidifiers with the only electrical component being the water solenoid. One humidifier works fine. The second one works but it consistently cuts out the furnace burner before the blower even comes on (less than minute). So there is a never-ending short cycle of one-minute burner only (with humidifier water solenoid energized), two minutes fan only, everything off for two minutes, then gas valve and humidifier solenoid both energized again until the gas valve prematurely closes and the burner turns off, etc. As soon as I disconnect the solenoid to the humidifier, the furnace will run normal cycles of 5, 10, 15, 20 minutes or whatever it takes to satisfy the thermostat. I have 27.2 volts to both gas valves when calling for heat. Both humidifier solenoids cause about a 1.5 voltage drop. The problem furnace's 24 volt circuit (gas valve and water solenoid) pulls a little more amperage than the combo that works well but ohms law tells me I am still only using about 14 watts between the valve and solenoid on the problem furnace and the 40VA transformer should handle that fine. (.2 amps gas valve plus .33 amps by the solenoid times 27.2 volts = about 14 watts).
Why will the gas valve not stay open when sharing its 24 VAC with the water solenoid? Am I barking up the wrong tree by thinking it is an electrical problem?
thanks,
cofloater

Comments (8)