Two single pole 40 amp breakers not physically tied together?

Chris Hansen
3 years ago

I have a circuit in my Square D service panel that serves the double wall oven. This circuit has 2 single pole 40 amp breakers, each with a 8 gauge wire into them that serves the oven. However, the two breakers' switch handles are not tied together. They can be physically turned off or on independent of the other. Should these two have a plastic piece or metal piece the connects the two breaker switch handles so they move together? Should I replace them with a double pole 40 amp breaker?