GFCI tripping
Comments (17)Hiring an electrician that has and knows how to use a megger will either prove or eliminate the underground as a problem. Many residential electricians haven't ever used one and get a "deer in the headlights" look when you ask about it. Additionally, the electrician should have a fault locater and know how to use it. Someone who knows how to use a fault locater can often pinpoint a leaky splice and may save you lots of landscaping damage. Underground splices correctly done with shrink sleeving that has a sealer inside provide a moisture proof splice and are perfectly safe in an otherwise code compliant installation. In residential applications I recommend running conduit specifically because of the issue you seem to be having, but there is no requirement to do so. The MINIMUM burial depth for either conduit or cable IF it has GFCI protection is 12" - - unless under 2" of concrete where 6" is acceptable or under 4" of concrete where 6" is acceptable for direct burial and 4" for conduit unless the concrete is a driveway, then 12" is required. 18" is the norm for burial and usually recommended absent unusual conditions. I'm not sure what braided wire is for use in conduit but there is stranded wire that is commonly used. Finally, be sure if you hire an electrician that (s)he doesn't have an issue with you providing material....See MoreCircuit not working except for one outlet and breaker not tripped
Comments (5)first, the fact that you replaced an outlet that was on an apparently unknown circuit underscores the importance of mapping all of the circuits in your house and always testing hot and neutral before touching them. if it had been a faulty outlet and you killed the power to the wrong circuit, it would have not been pleasant when you tried to replace the outlet. the first thing that came to mind with your description is that the one functioning outlet is the last in the series and the wires on the "load" side (so to speak, even though it isn't GFCI) somehow disconnected or the outlet itself is bad. that means everything on the other side of it won't work. just a thought. please don't touch any wires where there is a remote possibility that they are live. always test first....See MoreBreaker trips during thunderstorms
Comments (8)I guess I didn't make this quite clear. Replacing the breaker by itself isn't likely to make a difference. That's not the best place to start. To fix the problem, you have to remove the means for lightning to induce a surge in the circuit. The info about the age and weird wiring adds a dimension to this. You need to find any dead-end runs and ensure that they are isolated or, if possible, removed. My admittedly feeble EE sense is tingling - I'm thinking that old knob and tube might be more susceptible to surges because of the space between the conductors, but I could be wrong about that. We have some real EEs here who should be able to address that issue. I would start with having the electrical system grounding checked. Also make sure that any tall metallic objects (antenna masts, etc) are properly grounded. Then I'd rip out or isolate unused wiring. I'd fit a TVSS. The best ones mount at the meter itself, but in many cases the only way to get a meter-installed TVSS is through the power company with a monthly charge. A panel mounted device will suffice instead. Once you've found and corrected the real problem, THEN you replace the breaker, and only as a precaution because it may have been compromised by repeated trips....See Moreok to replace a dead-front gfci with gfci outlet?
Comments (16)Wow, what an old thread resurrected, but while it is here: If the tub manufacturer said it requires a dedicated circuit, then it needs to be a dedicated circuit by the code. All receptacles in the bathroom (with very small exception) have to be on the 20A circuit(s) that are either local to this bathroom alone or serve only other receptacles in other bathrooms. Just because you have one receptacle on this circuit doesn't give you free reign to have additional receptacles that don't meet these requirements. Based on the receptacle requirement, it's not uncommon to have the lights on a different circuit. Actually not uncommon from the days where GFCIs were expensive and they'd put all the bathroom receptacles (across multiple bathrooms) on a single GFCI. There's no rule about not putting receptacles near a toilet. All receptacles in bathrooms need GFCI protection....See MoreP b
5 years agoP b
5 years ago
Related Stories
DECORATING GUIDESTricks to Hide Light Switches, Outlets and Toilet Roll Holders
Embrace camouflage and other design moves to make these eyesores virtually disappear
Full StoryGREAT HOME PROJECTSPower to the People: Outlets Right Where You Want Them
No more crawling and craning. With outlets in furniture, drawers and cabinets, access to power has never been easier
Full StoryKITCHEN DESIGNKitchen Remodel Costs: 3 Budgets, 3 Kitchens
What you can expect from a kitchen remodel with a budget from $20,000 to $100,000
Full StoryDECORATING GUIDES12 Deadly Decorating Sins
Are your room designs suffering from a few old habits? It may be time to change your ways
Full StoryFUN HOUZZDon’t Be a Stickybeak — and Other Home-Related Lingo From Abroad
Need to hire a contractor or buy a certain piece of furniture in the U.K. or Australia? Keep this guide at hand
Full StoryKITCHEN CABINETSNew This Week: 3 Kitchens With Boldly Colored Cabinets
Ocean blue, timeless green and vibrant yellow hues create standout spaces
Full StoryKITCHEN DESIGNNew This Week: 3 Handsome Wood-and-White Kitchens
Wood brings warmth to kitchens in colder regions, while white walls and countertops keep things bright
Full StoryKITCHEN CABINETSNew This Week: 3 Modern Kitchens That Rock Warm Wood Cabinets
Looking for an alternative to bright white? Walnut cabinetry offers the perfect tone to warm things up
Full StoryKITCHEN DESIGNHere's Help for Your Next Appliance Shopping Trip
It may be time to think about your appliances in a new way. These guides can help you set up your kitchen for how you like to cook
Full StoryHOME OFFICESNew This Week: 3 Home Offices That Know How to Work It
We look at the designers’ secrets, ‘uh-oh’ moments and nitty-gritty details of 3 great home offices uploaded to Houzz this week
Full Story
kudzu9